Pregas Srinivasan <pregas@xxxxxxxxx>Date: Tue, Dec 27, 2011 at 9:10 AM
Subject: Re: [EnergyPlus_Support] Supply air temperature reset for peak hours
To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
Peak hours and Peak Days means your system (air side and water side) would be working at full capacity (unless you dont oversized them). Temperature reset strategy is a part load efficiency strategy and used to reduce energy consumption at part loads (for air side when outside air temperature = design air temperature, for chiller - reset water temperature reduces pump energy by reducing flow at each coils in proportion to load at each zones)
I am not familiar with Energy Plus, so i am not quite sure how to create a reset schedule.
Thanks,
Pregas Srinivasan
On Sat, Dec 24, 2011 at 12:07 PM, Amruta Khanolkar
<askhanol@xxxxxxx> wrote:
Hi All,
I am trying to reset Supply air temperature and Chilled water
temperature only for peak hours in peak days (4-5 days not the entire
year) in an Energy Plus model. For supply air temperature reset
strategy I added a new schedule at "schedule:compact" and assigned it
to :SetpointManager:Scheduled" where the previous schedule was
assigned. But finally I did not see any cooling reduction.
Am I missing something? Can you please tell me where and how should I do this?
Thank you for your help,
Amruta
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___