FYI: There is also quite a bit about pool modeling in the following references, enough so to actually predict the pool water use: Haberl, J., Claridge, D. 1987. “An Expert System for Building Energy Consumption Analysis: Prototype Results,” ASHRAE Transactions-Research,
Vol. 93, Pt. 1, pp. 979 - 998 (January). Haberl, J. 1986. “An Expert System for the Analysis of Building Energy Consumption,” Ph.D. Thesis, Department of Civil, Environmental and Architectural Engineering, University of Colorado at Boulder. This work was done at a Rec Center at the University of Colorado, which included a swimming pool (2 pools). The heat loss equations used the DeWinter approach.
Of importance to this discussion is the fact that the water that gets splashed out of the pool and/or gets carried off on the bodies of the swimmers when the exit the pool is often times larger than the evaporative loss.
The data used for the thesis contains almost 18 months of daily makeup water measurements that showed this trend. Also, you’ll need some sort of variable for
the filter type. In particular if it is a permanent media filter, there is a lot of water wasted to the drain when the filters are flushed. Finally, at the Rec Center in this 1986 study, the largest amount of water used was when they drained the pool each
for maintenance and cleaning, which was cut in half by draining one pool at a time while working on the pool and pumping the water from the full pool into the empty pool. Jeff 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=)8=? From:
EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Karen Walkerman Jim, Yes, I agree with what you say. I have modeled in the past many heated pools and always apply the evaporative losses to the pool heater, as this is the way it is dealt with in real life. An outdoor pool, or an unheated indoor pool lead
to much more complex interactions between the air mass and water mass. I think an outdoor pool would actually be easier to model as the pool itself will have very little impact on the air mass, and evaporation, radiation heating and cooling can be calculated
on an hourly basis. A pain in the ass, but achievable. An indoor space with un-regulated pool has a large impact on the air mass, so the heat balance needs to be calculated by an additive or iterative process (results from one timestep feeding the next). Much more difficult. -- Karen On Mon, Jan 9, 2012 at 2:10 PM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote: Dear Karen et al, As I think more about this, several things come to mind: ·
It’s a simple matter to calculate the amount of energy lost by evaporation; pool heater people have needed that information for a long time. It does not matter (to them) whether the energy for evaporation
is taken from the air or water; they just need to replace it. ·
For the purposes of pool water heating
energy calculations, it doesn’t matter where the energy goes either; the pool water heater must replace it. ·
I reached out to a colleague who is the Engineering Manager for one of the major pool dehumidification (air handler) companies to clarify this, since I did actually keep falling asleep in Thermodynamics class.
He says that essentially all of the heat of vaporization is removed from the pool’s water if the pool and surrounding air are the same temperature. (EngineeringToolBox.com says much the same, but my friend explained it better.) ·
For an unheated pool, the evaporation would cool the pool’s water and create some sensible temperature exchange between the pool and surrounding air. It will also change the
rate of evaporation. o
If the pool is heated and indoors, and the heater works properly, that won’t be true because the heater will act to maintain the water temperature at a constant value. o
If the pool is heated and outdoors, the rate of evaporation will change as the outdoor temp and humidity change. ·
The ASHRAE Handbook and my colleague reminded me about radiant heat transfer
to the sky (at night) or from the sky (actually solar energy) for an outdoor pool. These are aspects that I have no clue how to calculate. I hope they balance
J.
The Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Jim Dirkes
Enlightenment (much) appreciated! Perfect practical example! Thank you!
The Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Karen Walkerman
Hi James, Engineering ToolBox has a better explanation of pool heat transfer than I think I can give: Also, a little thought experiment - when you get out of a pool, and the surface of your skin is wet, as the water evaporates, you feel cool. Why? The evaporation of the water
must be removing heat from you, not just from the air around you. In the case of the pool, there is energy transfer from the pool, TO the evaporating water. If the surrounding space is very, hot then the evaporating water could also absorb heat from the
air, but this depends on the space temperature, the pool temperature and the vapor pressure in the space. Exactly how to split the cooling effect between the pool and the space, I'm not sure, but based on my understanding, under normal pool circumstances,
most of the cooling effect is applied to the body of water, not to the surrounding air. -- Karen On Sun, Jan 8, 2012 at 9:08 PM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
Karen, I kept falling asleep in Thermodynamics class, so I am not sure about this…. How could there be energy transfer to the pool water as a result of evaporation? I am having a hard time imagining it, or at least
imagining that it would be more than a tiny amount. Enlightenment welcome!
The Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Karen Walkerman
The other thing to consider is that the cooling due to evaporation will be split between the pool water and the space. Do you have the thermal mass of the pool water included in the space? This will help stabilize the air temperature. In this case you'd
also need to include your pool heat source into your zone heat balance. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.