RE: [EnergyPlus_Support] Heat Exchanger



Omar,



I agree with Karen here.  Note that the WaterHeater:* storage tanks have an input field called Source Side Effectiveness that provides simple model for just such a heat exchanger.



Brent



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Karen Walkerman
Sent: Thursday, January 19, 2012 8:15 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Heat Exchanger





Hi Omar,



I think the best way to do this is to connect the solar collectors to a Hot Water storage tank, and then connect the storage tank to the supply side of the second PlantLoop.  To get a pretty direct coupling between the two loops, make the storage tank volume small.  I have tried using the water/water heat exchanger for something other than free cooling with poor results.



--

Karen

On Thu, Jan 19, 2012 at 9:50 AM, Chandan Sharma <<mailto:csharma@xxxxxxxxxxxx>csharma@xxxxxxxxxxxx> wrote:



Omar,

Not sure about the answer to your question. The plate heat exchanger is basically meant to allow free cooling and thats how its operation scheme is set up internally in EnergyPlus.
But you can try connecting heat exchanger as you desire and see the results. If you are trying to model Integrated Collector Storage (ICS), this technology will be added to EnergyPlus in the upcoming release.
Sorry for the inconvenience.
Hope this helps.

Chandan


__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=23271/stime=1326991661>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmaDc1aDJ1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMjY5OTE2NjE->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkbXIxN3EzBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzI2OTkxNjYx>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___