The availability manager actually turns off the pump (or fan for air systems). So any equipment on that loop will be off.
On 1/27/2012 11:25 AM, Tooran T wrote:
thanks Dr.Li ,
i m not good at english so mybye i dont undrestand your word exactly .you say : " If the avilability manager is associated with the heater, it turns off the heater." and
" The size and type of the heater is another matter" what you mean by heater ?is that baseboard heater or water heater?
thank you very much Dr.Li
!- =============
Sizing:Plant,
Boiler Loop, !- Plant or Condenser Loop Name
HEATING, !- Loop Type
80., !- Design Loop Exit Temperature {C}
15; !- Loop Design Temperature Difference {deltaC}
!- ======================
is all you need to enter in the IDF. The size and type of the heater is another matter.
=============================
In control engineering most controller has a built in hysteresis. However, you may not be able to specify it exactly, if it is not designed to be adjustable.
What you are trying to do is to design your own controller.
Dr. Li
To:
energyplus_support@xxxxxxxxxxxxxxxFrom:
yli006@xxxxxxxxxxxDate: Fri, 27 Jan 2012 08:21:27 -0500
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
If the avilability manager is associated with the heater, it turns off the heater.
If the avilability manager is asspcoated with the tank used side, it turns off the loop supply (pump).
Sensor node need not be in the same loop, but must respond of the change when the control is activated. If the temperature falls below the limit, the control is removed. Back to your thermostat problem. Set-back is not the same as limits.
Dr. Li
To:
EnergyPlus_Support@xxxxxxxxxxxxxxxFrom:
t.t111ir@xxxxxxxxxDate: Fri, 27 Jan 2012 09:36:16 +0000
Subject: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
Dear memebers ,
ref : Document :EngineeringRefrence.pdf -983
"High temperature turn off :
The input object availabilityManager:High temperaturTurnoff is used to turn off a central air system or a plant loop if a sensed node temperature exceeds a temperature limit."
i want to know availabilityManager:High temperaturTurnoff , turn off the plant loop or just the turn off the component ?
for example : i set field :Sensor Node name : at the outlet of boiler .. in this plant loop there is pump and boiler as a component.
then availabilityManager:High temperaturTurnoff turn off boiler or plant loop ?if it turn off the plant loop it means it turned off pump too?
thanks
--