[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff





i want to :
if inlet water pump > 65C then pump will be off
and if inlet water pump < 65 then pump will be on
 
for this type of controling can we use two availabilityManager:
 
one availabilityManager:High temperaturTurnoff  :for  inlet water pump > 65C then pump will be off .
and another availabilityManager: low temperaturTurnon : for inlet water pump < 65 then pump will be on.
is that right?
thanks
 
 
From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Friday, January 27, 2012 8:12 PM
Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff

 
The availability manager actually turns off the pump (or fan for air systems). So any equipment on that loop will be off.

On 1/27/2012 11:25 AM, Tooran T wrote:
 


From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Friday, January 27, 2012 7:31 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff

  thanks Dr.Li ,
i m not good at english so mybye i dont undrestand your word exactly  .you say : "  If the avilability manager is associated with the heater, it turns off the heater." and
" The size and type of the heater is another matter" what you mean by heater ?is that baseboard heater or water heater?
 
thank you very much Dr.Li
!- =============
  Sizing:Plant,
Boiler  Loop, !- Plant or Condenser Loop Name
HEATING, !- Loop Type
80., !- Design Loop Exit Temperature {C}
15; !- Loop Design Temperature Difference {deltaC}
!- ======================
 
is all you need to enter in the IDF.  The size and type of the heater is another matter.
=============================
In control engineering most controller has a built in hysteresis.  However, you may not be able to specify it exactly, if it is not designed to be adjustable. 
 
What you are trying to do is to design your own controller.
 Dr. Li  

 
To: energyplus_support@xxxxxxxxxxxxxxx
From: yli006@xxxxxxxxxxx
Date: Fri, 27 Jan 2012 08:21:27 -0500
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff

 
If the avilability manager is associated with the heater, it turns off the heater.
 
If the avilability manager is asspcoated with the tank used side, it turns off the loop supply (pump).
 
Sensor node need not be in the same loop, but must respond of the change when the control is activated.  If the temperature falls below the limit, the control is removed.  Back to your thermostat problem.   Set-back is not the same as  limits.

 Dr. Li  

 
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: t.t111ir@xxxxxxxxx
Date: Fri, 27 Jan 2012 09:36:16 +0000
Subject: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff

 
Dear memebers ,
ref : Document :EngineeringRefrence.pdf -983
"High temperature turn off :
The input object availabilityManager:High temperaturTurnoff is used to turn off a central air system or a plant loop if a sensed node temperature exceeds a temperature limit."

i want to know availabilityManager:High temperaturTurnoff , turn off the plant loop or just the turn off the component ?
for example : i set field :Sensor Node name : at the outlet of boiler .. in this plant loop there is pump and boiler as a component.

then availabilityManager:High temperaturTurnoff turn off boiler or plant loop ?if it turn off the plant loop it means it turned off pump too?

thanks






-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___