|
I tried your IDF which was extracted from your hotmail.
The sorted file, the .csv and the error files are attached. As you are using DesignBuilder or some other third party software, the warnings are expected. You have a simple one zone building. The result showed that the coooling and heating are not properly applied. The location seems to be in London, England. The simulation was done without the weather file. 1) If the building is not accurate in construction, the reasult will be meaning less. Is it a simple one storey rectangular building with no partitions? Where are the radiators, and plant rooms? 2) The windows and doors shuld be in actual position, facing the correct orientation for solar radiation calculation. Blinds should be specified, if used. 3) Ceiling insulatin and roof design are important. I do not think, it is flat. 4) Schedules many not be correct. for turning on the system and the lights, etc. You also have mixed long and compact formats. 5) No domestic hot water usuage in the simulation. Two boilers may not give you savings. Each warning in the error file would give you something to think about. It is common for DesignBuider to provide unavailaable and un-necessary output variable request. Over one hundred were selected. DesignDay simulation does not give you monthly and annual values, and I usually do not use them as they do not provide information at the debugging state. =============== When you do a simulation, you must have a plan in your own or plain language. Occupancy: Peple number, period of day present. etc. Who are these people. Some would move in and out, some may be permanent in the building. When to turn on the lights and equipment. These can be verified with schedule value in the .csv. Natural temperature output , add some venilation, to verify the building construction. System node temperature to verify the equipment operaton. =============== Use the .rdd file to select the report variable entries. Make all the display in timestep. No need to run the weather file, until you have sorted out what to include in the IDF. ===================== When you have many radiators with a valve, it is like the diffusers with a damper. Because they are all in one room, you can use just one radiator. The zone thermostat will be use to simulate the manual valve setting. The circulating pump is set very high. You can reduce it later to see the effect. Boiler is not set to operate between 82 and 72°C. I have not yet look at the system node values. The availability manager and the schedules may lock the system out. There is no cooling and exter ventilation in Summer. Winter sun is turned off by cloud. ====================== YOu need to learn to find all these by reading the .csv file and turning on the diagnostics. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sat, 28 Jan 2012 13:33:53 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff Dear Dr.Li ,
I m master of science mechanical engineering, and it is my project to simulate one building that my profesor show me , i do experimental on that building , and in my project i must simulate it and then i suggest some good saving energy method , in this building there is one boiler for hot water radiator and domostic hot water , one
way that i suggest that there is two boiler for this two aim one is for domostic hot water and another is for hot water that result to saving energy , by the way im female not male .
Dear Dr.Li as exactly you say
You do not see or use a thermostat in the room, it is because the user is the termostat.
There is manual valve on the radiator. Some of them are calibrated in temperature or just an marker. The occupant will adjust that to suit their comfort. i dont use VAV HVAC System ,
In the real system, the pump by-pass has a non return valve. When the pump is working the pipe is closed. When the return water temperature falls to below the set point, the pump is stopped, and the water flows through the by-pass.
and exactly it is my system . in this building for example in summer because outside weather is hot for saving energy the don use pump , the get out pump amn use bypass. i think in energyplus i cant use bypass with supply pump.
you mean when there is no thermostat how i must enter in thermostat heating setpoint in energyplus ?
in my building this radiator in room with out thermostat
very very vry special thanks
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Saturday, January 28, 2012 4:18 PM Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff There are many components in an old system that is very efficient. You do not see or use a thermostat in the room, it is because the user is the termostat. There is manual valve on the radiator. Some of them are calibrated in temperature or just an marker. The occupant will adjust that to suit their comfort. I do not know why we talk about energy saving and yet want to throw away all the cost saving system. There is no need to have VAV VRV HVAC system. Most of them are not energy efficient. I now understand why most new users are using the VAV tmplate and VAV zone equipment, because that was in the Gertting Started exercise. =============================== For T.T's IDF, you can remove the first two objects on availabilityManager:.. . They will not work as you intended. Have a closer look at your Iran system. You may be still missing some good features. In the real system, the pump by-pass has a non return valve. When the pump is working the pipe is closed. When the return water temperature falls to below the set point, the pump is stopped, and the water flows through the by-pass. In the London furnace, there is a safety valve with steam whistle. The water temperature is controlled by chimney damper setting and the fire air inlet size. Again, there was no thermostat. When the temperature is too high, all occupants would notice and would go to the furnace to shut it down, or call the attendant. No thermostat, does not mean that there is no control. Dr. Li.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Fri, 27 Jan 2012 22:09:44 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff yes exactly we use pump by bypass mode . what do you mean by different algorithm?
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Friday, January 27, 2012 10:24 PM Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff If you turn on and off the pump at 65°C, to implement the pump by pass mode. Again, it is a different algorithm. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Fri, 27 Jan 2012 18:43:08 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff i want to :
if inlet water pump > 65C then pump will be off
and if inlet water pump < 65 then pump will be on
for this type of controling can we use two availabilityManager:
one availabilityManager:High temperaturTurnoff :for inlet water pump > 65C then pump will be off .
and another availabilityManager: low temperaturTurnon : for inlet water pump < 65 then pump will be on.
is that right?
thanks
From: Richard Raustad <RRaustad@xxxxxxxxxxxx> To: EnergyPlus_Support@xxxxxxxxxxxxxxx Sent: Friday, January 27, 2012 8:12 PM Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff The availability manager actually turns off the pump (or fan for air systems). So any equipment on that loop will be off. On 1/27/2012 11:25 AM, Tooran T wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |
Attachment not found: d:\eudora\attach\Toolan01DD.csv
Attachment not found: d:\eudora\attach\Toolan01DD.err
Attachment not found: d:\eudora\attach\Toolan01DD.idf