I tried your IDF which was extracted from your hotmail.
The sorted file, the .csv and the error files are attached. As you are using DesignBuilder or some other third party software, the warnings are expected.
You have a simple one zone building. The result showed that the coooling and heating are not properly applied. The location seems to be in London, England. The simulation was done without the weather file.
1) If the building is not accurate in construction, the reasult will be meaning less. Is it a simple one storey rectangular building with no partitions? Where are the radiators, and plant rooms?
2) The windows and doors shuld be in actual position, facing the correct orientation for solar radiation calculation. Blinds should be specified, if used.
3) Ceiling insulatin and roof design are
important. I do not think, it is flat.
4) Schedules many not be correct. for turning on the system and the lights, etc. You also have mixed long and compact formats.
5) No domestic hot water usuage in the simulation. Two boilers may not give you savings.
Each warning in the error file would give you something to think about.
It is common for DesignBuider to provide unavailaable and un-necessary output variable request. Over one hundred were selected. DesignDay simulation does not give you monthly and annual values, and I usually do not use them as they do not provide information at the debugging state.
===============
When you do a simulation, you must have a plan in your own or plain language.
Occupancy: Peple number, period of day present. etc. Who are these people.
Some would move in and out,
some may be permanent in the building.
When to turn on the lights and equipment. These can be verified with schedule value in the .csv.
Natural temperature output , add some venilation, to verify the building construction.
System node temperature to verify the equipment operaton.
===============
Use the .rdd file to select the report variable entries. Make all the display in timestep.
No need to run the weather file, until you have sorted out what to include in the IDF.
=====================
When you have many radiators with a valve, it is like the diffusers with a damper.
Because they are all in one room, you can use just one radiator. The zone thermostat will be use to simulate the manual valve setting.
The circulating pump is set very high. You can reduce it later to see the effect. Boiler is not set to operate between
82 and 72°C. I have not yet look at the system node values. The availability manager and the schedules may lock the system out.
There is no cooling and exter ventilation in Summer. Winter sun is turned off by cloud.
======================
YOu need to learn to find all these by reading the .csv file and turning on the diagnostics.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: t.t111ir@xxxxxxxxx
Date: Sat, 28 Jan 2012 13:33:53 +0000
Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
Dear Dr.Li ,
I m master of science mechanical engineering, and it is my project to simulate one building that my profesor show me , i do experimental on that building , and in my project i must simulate it and then i suggest some good saving energy method , in this building there is one boiler for hot water radiator and domostic hot water , one
way that i suggest that there is two boiler for this two aim one is for domostic hot water and another is for hot water that result to saving energy , by the way im female not male .
Dear Dr.Li as exactly you say
You do not see or use a thermostat in the room, it is because the user is the termostat.
There is manual valve on the radiator. Some of them are calibrated in temperature or just an marker. The occupant will adjust that to suit their comfort.
i dont use VAV HVAC System ,
In the real system, the pump by-pass has a non return valve. When the pump is working the pipe is closed. When the return water temperature falls to below the set point, the pump is stopped, and the water flows through the by-pass.
and exactly it is my system . in this building for example in summer because outside weather is hot for saving energy the don use pump , the get out pump amn use bypass.
i think in energyplus i cant use bypass with supply pump.
you mean when there is no thermostat how i must enter in thermostat heating setpoint in energyplus ?
in my building this radiator in room with out thermostat
very very vry special thanks
From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Saturday, January 28, 2012 4:18 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
There are many components in an old system that is very efficient.
You do not see or use a thermostat in the room, it is because the user is the termostat.
There is manual valve on the radiator. Some of them are calibrated in temperature or just an marker. The occupant will adjust that to suit their comfort.
I do not know why we talk about energy saving and yet want to throw away all the cost saving system.
There is no need to have VAV VRV HVAC system. Most of them are not energy efficient.
I now understand why most new users are using the VAV tmplate and VAV zone equipment, because that was in the Gertting Started exercise.
===============================
For T.T's IDF, you can remove the first two objects on availabilityManager:.. . They will not work as you intended.
Have a closer look at your Iran system. You may
be still missing some good features.
In the real system, the pump by-pass has a non return valve. When the pump is working the pipe is closed. When the return water temperature falls to below the set point, the pump is stopped, and the water flows through the by-pass.
In the London furnace, there is a safety valve with steam whistle. The water temperature is controlled by chimney damper setting and the fire air inlet size. Again, there was no thermostat. When the temperature is too high, all occupants would notice and would go to the furnace to shut it down, or call the attendant.
No thermostat, does not mean that there is no control.
Dr. Li.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: t.t111ir@xxxxxxxxx
Date: Fri, 27 Jan 2012 22:09:44 +0000
Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
yes exactly we use pump by bypass mode . what do you mean by different algorithm?
From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Friday, January 27, 2012 10:24 PM
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
If you turn on and off the pump at 65°C, to implement the pump by pass mode. Again, it is a different algorithm.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: t.t111ir@xxxxxxxxx
Date: Fri, 27 Jan 2012 18:43:08 +0000
Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
i want to :
if inlet water pump > 65C then pump will be off
and if inlet water pump < 65 then pump will be on
for this type of controling can we use two availabilityManager:
one availabilityManager:High temperaturTurnoff :for inlet water pump > 65C then pump will be off .
and another availabilityManager: low temperaturTurnon : for inlet water pump < 65 then pump will be on.
is that right?
thanks
From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Friday, January 27, 2012 8:12 PM
Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
The availability manager actually turns off the pump (or fan for air systems). So any equipment on that loop will be off.
On 1/27/2012 11:25 AM, Tooran T wrote:
thanks Dr.Li ,
i m not good at english so mybye i dont undrestand your word exactly .you say : " If the avilability manager is associated with the heater, it turns off the heater." and
" The size and type of the heater is another matter" what you mean by heater ?is that baseboard heater or water heater?
thank you very much Dr.Li
!- =============
Sizing:Plant,
Boiler Loop, !- Plant or Condenser Loop Name
HEATING, !- Loop Type
80., !- Design Loop Exit Temperature {C}
15; !- Loop Design Temperature Difference {deltaC}
!- ======================
is all you need to enter in the IDF. The size and type of the heater is another matter.
=============================
In control engineering most controller has a built in hysteresis. However, you may not be able to specify it exactly, if it is not designed to be adjustable.
What you are trying to do is to design your own controller.
Dr. Li
To:
energyplus_support@xxxxxxxxxxxxxxxFrom:
yli006@xxxxxxxxxxxDate: Fri, 27 Jan 2012 08:21:27 -0500
Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
If the avilability manager is associated with the heater, it turns off the heater.
If the avilability manager is asspcoated with the tank used side, it turns off the loop supply (pump).
Sensor node need not be in the same loop, but must respond of the change when the control is activated. If the temperature falls below the limit, the control is removed. Back to your thermostat problem. Set-back is not the same as limits.
Dr. Li
To:
EnergyPlus_Support@xxxxxxxxxxxxxxxFrom:
t.t111ir@xxxxxxxxxDate: Fri, 27 Jan 2012 09:36:16 +0000
Subject: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff
Dear memebers ,
ref : Document :EngineeringRefrence.pdf -983
"High temperature turn off :
The input object availabilityManager:High temperaturTurnoff is used to turn off a central air system or a plant loop if a sensed node temperature exceeds a temperature limit."
i want to know availabilityManager:High temperaturTurnoff , turn off the plant loop or just the turn off the component ?
for example : i set field :Sensor Node name : at the outlet of boiler .. in this plant loop there is pump and boiler as a component.
then availabilityManager:High temperaturTurnoff turn off boiler or plant loop ?if it turn off the plant loop it means it turned off pump too?
thanks
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years