[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Max Iterations exceeded?





SizingPeriod:WeatherFileConditionType,

WinterDesignDay, !- Name

WinterExtreme, !- Period Selection

WinterDesignDay, !- Day of Week for Start Day

No, !- Use Weather File Daylight Saving Period

Yes; !- Use Weather File Rain and Snow Indicators

SizingPeriod:WeatherFileConditionType,

SummerDesignDay, !- Name

SummerExtreme, !- Period Selection

SummerDesignDay, !- Day of Week for Start Day

No, !- Use Weather File Daylight Saving Period

Yes; !- Use Weather File Rain and Snow Indicators
========================
 
I have never defined SummerDesignDay and WinterDesignDay in this way.  So I cannot comment on what is happening.
 
I debug the system usually  using a 24 hour timestep data. 
 
The traces does not show much detail, and the general trends are correct.
 
The outdoor air temperature and the zone mean air temperature were not shown.
 
The IDF is generated from OpenStudio, that is why is so large in size.  I am not used to this format.  You are using VAV as well.  The sechedules for DesignDay were not specifically defined.
 
 
 
Dr. Li  

 


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: gch2j2006@xxxxxxxxx
Date: Fri, 3 Feb 2012 08:24:39 -0800
Subject: Re: [EnergyPlus_Support] Max Iterations exceeded?

 
Dr Li-True. That is the first the cooling is turned on but it concerns me because big zones that I have called out for, their coils are sizing to be zero.  I've attached both the IDF and a csv file of the output variables I've been looking at.

In the csv file, if you look at chart 6, it is graphing the heating setpoints (in red), cooling setpoints (in green) along with the zone air temperature (in blue) for the two summer and winter design days. Everything is within the setpoints there.

Chart 7 graphs the same but during a month (July) typical for cooling. The blue line is always out of range for the cooling setpoints that I've specified.

Chart 8 graphs a month typical for heating (January) and the same thing happens. The schedules are not exactly what I want (but close enough) and the units don't seem to be meeting the demand of the zone enough to heat and cool the areas.  Any thoughts?


From: YuanLu Li <yli006@xxxxxxxxxxx>
To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Thursday, February 2, 2012 2:20 PM
Subject: RE: [EnergyPlus_Support] Max Iterations exceeded?

 
The reporting time is June 01 at 08:00 am.  If this is the first time the cooling is turned on, you can ignore the warning.
 
If you get lots of these, there may be some incorrect sizing or scheduling program. 
 
The zone mean temperature  and system cooling and heating rate  usually will give the clue.
 
The long report simply says that the cooling plant is not turned on at that time, which could be at the heating and cooling change over point, if you have mixed thermostat types in use.
 
I cannot tell the problem by looking the error message alone.

 Dr. Li  

 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: gch2j2006@xxxxxxxxx
Date: Thu, 2 Feb 2012 18:10:54 +0000
Subject: [EnergyPlus_Support] Max Iterations exceeded?

 
I've been getting messages like this a lot. Wondering if anyone could help me out (Dr Li? Anyone?)

** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at SDD, 06/01 08:00 - 08:06
** ~~~ ** SimFlags=[TFFFF] AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],ElecCircuits[F]..F=ok,T=fail
** ~~~ ** HVAC Tolerance Flags=[0000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
** ~~~ ** HVAC Tolerance Values, Most Recent listed first
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[610 - 0 CLASSROOMS RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=1.478E-011, HumRatTol=1.7347E-018, PressureTol=3.E-011
** ~~~ ** FlowQualTol=0.00, EnergyTol=3.135E-007, TempTol=3.55E-015
** ~~~ ** HVAC side outlet node=[609 - 5 OTHERS RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[608 - 5 LABS RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[607 - 5 CLASSROOMS RETURN AIR OUTLET]
** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** HVAC side outlet node=[606 - 4 OTHERS RETURN AIR OUTLET]
** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
** ~~~ ** Plant Tolerance Values, Most Recent listed first
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[337 - CHILLED WATER PLANT CNDW SUPPLY OUTLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[345 - CHILLED WATER PLANT CNDW DEMAND OUTLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[327 - CHILLED WATER PLANT CHW SUPPLY OUTLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[301 - HOT WATER PLANT HW SUPPLY OUTLET]
** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
** ~~~ ** Plant side outlet node=[333 - CHILLED WATER PLANT CHW DEMAND OUTLET]
** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first

I've tried changing different setpoints and messing with my schedules but nothing seems to work. The result of this is mostly that none of my zones receive the proper cooling (all the cooling coils have a nominal capacity of 0) and I see no end uses in cooling after the simulation.







__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___