Re: [EnergyPlus_Support] Problems modeling a chiller



Hi,
finally I recalculated the performance curves and now the model is
working.I had to set the condenser delta temperature to 5K because I
had the leaving water condenser temperature provided by the
manufacturer but I need the entering condenser temperature in order to
model my chiller as Chiller:ElectricEIR.
Now I'm focusing on how E+ control the chiller plant.I found a new
variable for me:
Chiller False Load Heat Trans [J]
I understand it as wasting energy variable in order to met the cooling
capacity supplied by the chiller and the required load supplied by the
chilled water loop.
I have been reading the EngineeringReference.pdf(page 550-55) but I
have no any clear idea how E+ controls the plant.
If I see the performance curves,they show that the chiller works
better with PLR and my simulation shows in the wrong way,when the HVAC
is working for low PLR the COP is very low.
Could someone explain me it better?
Thanks,
Ignacio Gomis
P.S.:I will attack the performance curve spreadsheet,the idf file, its
rvi file and the csv file which is the result of the simulation.

On 9 February 2012 16:24, Nacho Gomis <nachogo27@xxxxxxxxx> wrote:
> Without looking at your file?
> ·         Does the pump have sufficient flow to properly transfer the 1MW?
> Well,1MW is the cooling capacity,so the condenser will have a higher
> value but never be 2MW.The pump flow rate is manually sized because
> this data is provided by the chiller manufacturer,the value is
> 0.05743m3/s and it is used in the corresponding field in the
> ElectricChiller:ReformulatedEIR object.(Chiller model:Carrier 30XW
> 1002)
>
> ·         Is the pump operating? (schedule = 1.0)
> Yes,i have not scheduled the pump.It works fine with the template chiller
> ·         Is the tower operating?
> Yes,it has cooling capacity because I can see it in the output that
> Richard told me in the message above.
>
> Thanks,
> Ignacio Gomis


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


Content-Type: application/vnd.openxmlformats-officedocument.spreadsheetml.sheet; 
	name="PFC_v7_L-V-FC-AC-30XA1002_exp(MinUnl0,15).xlsx"
Content-Disposition: attachment; 
	filename="PFC_v7_L-V-FC-AC-30XA1002_exp(MinUnl0,15).xlsx"
X-Attachment-Id: f_gyhhy24v0

Content-Type: application/octet-stream; 
	name="PFC_v7_L-V-FC-AC-30XA1002_exp.idf"
Content-Disposition: attachment; 
	filename="PFC_v7_L-V-FC-AC-30XA1002_exp.idf"
X-Attachment-Id: f_gyhhyahr1

Content-Type: application/octet-stream; 
	name="PFC_v7_L-V-FC-AC-30XA1002_exp.rvi"
Content-Disposition: attachment; 
	filename="PFC_v7_L-V-FC-AC-30XA1002_exp.rvi"
X-Attachment-Id: f_gyhhyaht2

Content-Type: application/vnd.openxmlformats-officedocument.spreadsheetml.sheet; 
	name="Chiller_PerformanceCurve_Coefficients_30XA-1002(Elim45).xlsx"
Content-Disposition: attachment; 
	filename="Chiller_PerformanceCurve_Coefficients_30XA-1002(Elim45).xlsx"
X-Attachment-Id: f_gyhhyk2m3
Attachment not found:
d:\eudora\attach\PFC_v7_L-V-FC-AC-30XA1002_exp(MinUnl0,15).xlsx
Attachment not found:
d:\eudora\attach\PFC_v7_L-V-FC-AC-30XA1002_exp.idf
Attachment not found:
d:\eudora\attach\PFC_v7_L-V-FC-AC-30XA1002_exp.rvi
Attachment not found:
d:\eudora\attach\Chiller_PerformanceCurve_Coefficients_30XA-1002(Elim45).xlsx