Simulation will do whatever you ask the program to do.
It is not necessary to provide a by-pass. You can use a pump which has a low head to simulate the natural flow. You can look at the .rdd and see what is available. If there is a flow rate through the bypass in the output variable, you can monitor that. If a branch or component has an available schedule, it can be scheduled. Scheduling need not be automatic. If your caretaker turns on and off the pump manually every morning after starting the furnace, you will schedule both these activities. The house hold thermostat has mercury switch module with two contacts mounted on a temperature sensing element. There is also a fan speed control (off, 1,2,3), heat/cool control, and a thermometer. All these are simulated separately, as sensor, controller or actuator, and selectors. ====== You can use the pump mass flow rate variable to show that the pump is working. This is monitoring process. Scheduling is a control process. Sense and then actuate is a controller manager action. ===================== If your are worried about the power consumption, simply reduce the head. The circulation pump is not a large element, unless you need to lift the water to a very high level into an open tank. When all the radiators are turned off in Summer, the pump will only pumping the DHW heater. You can sense the DHW temperature and force the pump on again, if necessary. =================== How to turn the radiators off? Do you know how it is done? You were only simulating during the Winter months of the weather file. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Wed, 15 Feb 2012 10:46:39 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff can i use pump flow rate schedule to show some times pump is out of work and water flows in bypass branch ?
From: Tooran T <t.t111ir@xxxxxxxxx> To: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx> Sent: Wednesday, February 15, 2012 10:16 AM Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff I do not understand your question or the purpose of the moving of the pump position.
In your PDF diagram, the pump is in the orage coloured pipe, lower temperature return pipe. This is the position in the SVG diagram, and is the recommended branch ordering. It is possible to move the pump to the demand side inlet, but you should ask the support group, if the simulation fails.
The SVG diagram looks fine, although it is not the usual view, which begins with a pump without a by-pass path. use bypass with pump , in example files of energyplus i see it use boiler branch with bypass , but in my idef i use pump branch with bypass branch .
in summer or some times of the year that produces the pressure difference due to temperature difference ,(natural circulating with out need pump )
we use bypass mode and pump is out of the work , how can i show this in simulation in energyplus ?( i want to say use bypass branch instead of pump in summer ) -----------------------------------------------------------------------------------------
in OBJECTS IN CLASS: WATERHEATER:MIXED
WaterHeater:Mixed,
Indirect Water Heater, !- Name AUTOSIZE, !- Tank Volume {m3} water heater Setpoint Temperature Schedule, !- Setpoint Temperature Schedule Name field: Setpoint Temperature , determines when heater of the water heater will be on and off ,is that right?
but in ALL OBJECTS IN CLASS: BOILER:HOTWATER, there is no Setpoint Temperature Schedule field to determines when burner of boiler will be on and off , how can i control the burner of boiler?does setpoint temperature in pLant loop(hot water plant loop) controls burner of boiler ?
the setpoint temperature for plant loops it means it controls the whole plant (pump , boiler )?
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.