|
Hi, T.T
When yhe object asks you to enter a schedule, you can provide one. Otherwise, you must provide your own controller, manager, etc. The boiler temperature is set in the object as shown in red below. ================== Boiler:HotWater, Central Boiler, !- Name NaturalGas, !- Fuel Type autosize, !- Nominal Capacity {W} 0.8, !- Nominal Thermal Efficiency , !- Efficiency Curve Temperature Evaluation Variable linear, !- Normalized Boiler Efficiency Curve Name 80, !- Design Water Outlet Temperature {C} autosize, !- Design Water Flow Rate {m3/s} 0, !- Minimum Part Load Ratio 1.2, !- Maximum Part Load Ratio 1.0, !- Optimum Part Load Ratio Central Boiler inlet Node, !- Boiler Water Inlet Node Name Central Boiler Outlet Node, !- Boiler Water Outlet Node Name 100., !- Water Outlet Upper Temperature Limit {C} ConstantFlow; !- Boiler Flow Mode Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Thu, 16 Feb 2012 11:24:03 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff Dr.Li it is very strange i use setpoint manager for HW plant such as below :
HW supply Outlet Node, !- Loop Temperature Setpoint Node Name
HW Loop Temp Schedule, !- Schedule Name
HW supply Outlet Node; !- Setpoint Node or NodeList Name Schedule:Compact,
HW Loop Temp Schedule, !- Name Temperature, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Alldays, !- Field 2
Until: 24:00, 75; !- Field 4 the result are the same when i use
HW supply inlet Node, !- Loop Temperature Setpoint Node Name
You have not set the schedule: Hot Water Setpoint Temperature Schedule, in !- ======================= The name in your compact scedule was not the same. i see in winter design day when inlet boiler temperature greater than 75 then it off the boiler in both case. The boiler will go off when the radiators are all off and the DHW tank has reached 75°C, or whatever you set in the program.
i dont undrestand why there is no differenc between them
thanks for your attention
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Wednesday, February 15, 2012 3:16 AM Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff I do not understand your question or the purpose of the moving of the pump position.
In your PDF diagram, the pump is in the orage coloured pipe, lower temperature return pipe. This is the position in the SVG diagram, and is the recommended branch ordering. It is possible to move the pump to the demand side inlet, but you should ask the support group, if the simulation fails.
The SVG diagram looks fine, although it is not the usual view, which begins with a pump without a by-pass path. The Winter operation seems correct. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Tue, 14 Feb 2012 09:16:33 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff Dear Dr.Li ,
could you please see the file that i attached it ?
there is pump as first object in supply side in example files of energyplus , i want to know there is problem if i use pump after water heater ?
there is no problem in energyplus simulation that i use bypass with pump ?
thanks
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Saturday, January 28, 2012 4:08 AM Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff Algorithm is used to design a software for simulation. In the earlier version of EPlus, I seem to remember, there was a pump by-pass. The newer version does not seem to have that in the examples of the example file. The work around is to leave the pump in and reduce the pressure to a smaller value to reflect the temperature difference of the up and down pipes which created a pressure difference. Simulate it without the by-pass and see how much is the pump power. If it is not significant, simply ignore the pump power. You cannot really stop the pump, as the equation used for simulation requires a pressure difference to circulate the water. Therefore, instead of using a pump, you will have substitute the equation with one that produces the pressure difference due to temperature difference. This is what I meant by changing the algorithm in simulation. The tank can be controlled to the 80 - 65 range without the pump control. The zone thermotat if is a common one would turn on and off the pump for all the radiators. In this case you will not have a thermostat control in each room. If the room have different thermal characteristics, the EPlus simulation will show the differences in room temperature. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Fri, 27 Jan 2012 22:09:44 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff yes exactly we use pump by bypass mode . what do you mean by different algorithm?
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Friday, January 27, 2012 10:24 PM Subject: RE: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff If you turn on and off the pump at 65°C, to implement the pump by pass mode. Again, it is a different algorithm. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Fri, 27 Jan 2012 18:43:08 +0000 Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff i want to :
if inlet water pump > 65C then pump will be off
and if inlet water pump < 65 then pump will be on
for this type of controling can we use two availabilityManager:
one availabilityManager:High temperaturTurnoff :for inlet water pump > 65C then pump will be off .
and another availabilityManager: low temperaturTurnon : for inlet water pump < 65 then pump will be on.
is that right?
thanks
From: Richard Raustad <RRaustad@xxxxxxxxxxxx> To: EnergyPlus_Support@xxxxxxxxxxxxxxx Sent: Friday, January 27, 2012 8:12 PM Subject: Re: [EnergyPlus_Support] availabilityManager:High temperaturTurnoff The availability manager actually turns off the pump (or fan for air systems). So any equipment on that loop will be off. On 1/27/2012 11:25 AM, Tooran T wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |