[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] setpoint manager





thanks Karen ,
i have another question that maybye is not related to setpoin manager ,
if burner of boiler is on when its hot water temperature greater than 80C then how can i set this in enegyplus ?
is that the field : design water outlet temperature in boiler class ?
 
 

From: Karen Walkerman <kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, February 21, 2012 7:29 PM
Subject: Re: [EnergyPlus_Support] setpoint manager

 
Hi Tooran,

I'm not sure if there is equipment capable of maintaining a temperature at the supply inlet node.  In real life this could be done by matching the plant heat output and the pump speed to the energy demand, but I'm not sure how you'd achieve this in EnergyPlus.  I've never had to model a system this way.  You could probably achieve it using the Energy Management System.

--
Karen

On Tue, Feb 21, 2012 at 10:54 AM, Tooran T <t.t111ir@xxxxxxxxx> wrote:
 
thanks Karen , it is good explanation :)
but  for example if i set the PlantLoop Supply inlet Node to maintain a certain temperature,  then what happens ?

From: Karen Walkerman <kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, February 21, 2012 7:13 PM
Subject: Re: [EnergyPlus_Support] setpoint manager

 
A SetpointManager is basically a control point - it indicates the status to be maintained at that point in the loop.  For example, if you set the PlantLoop Supply Outlet Node to maintain a certain temperature, the equipment on the supply side of the plant loop will need to operate to maintain that temperature.  If the PlantLoop is a hot water loop and there is a boiler on the supply side, then the boiler might modulate to maintain the setpoint temperature.  Not all equipment is capable of maintaining all setpoints, so sometimes the setpoint is not met and other problems can result, but think about it as a desired state within the plantloop controls.

--
Karen

On Tue, Feb 21, 2012 at 10:36 AM, Tooran <t.t111ir@xxxxxxxxx> wrote:
 
Hi ,
i read this about setpoint manager in I/O ref :
setpoint manager are one of the high level control construct in energyplus. A setpoint manager is able to access data from any of the hvac system nodes and use this data to calculate a setpoint for one or more other hvac system nodes.setpoints are then used by controllers or plant or condenser loops as goal for their control action ....."

but i dont undrestand it well especialy use of setpoint in the case of plant loop , could you please describe it please?

thanks









__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___