Re: [EnergyPlus_Support] DDY files





You might run your simulation, then find the peak heating & cooling day(s) then use the "sizeing period weather file days" object to do your sizeing wthout the DDY file.

Name cool
Begin Month 7
Begin Day of Month 21
End Month 7
End Day of Month 21
Day of Week for Start Day SummerDesignDay
Use Weather File Daylight Saving Period Yes
Use Weather File Rain and Snow Indicators Yes

Name heat
Begin Month 12
Begin Day of Month 21
End Month 12
End Day of Month 21
Day of Week for Start Day WinterDesignDay
Use Weather File Daylight Saving Period Yes
Use Weather File Rain and Snow Indicators Yes






On Mon, Mar 5, 2012 at 10:25 AM, moh_alyetman <moh_alyetman1@xxxxxxxxxxx> wrote:
 

I am looking for Jeddah Saudi Arabia but the one I found is empty "No Design Conditions found for this Location". Can any one help ?
How can I create it or edit another one?

Thank you.




--
Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
www.cleantechanalytics.com


This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___