How about setting the Controller:OutdoorAir for a specific minimum flow, something like: p.s., EnergyPlus expects flow rates in m3/s. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hnoboam I need to simulate a stuck open economizer damper. To do this I thought I could use an EMS program to override the outdoor air flow rate setpoint. Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.