[EnergyPlus_Support] Re: Air Cooled Condenser Inlet Temperature below 0C



Thanks, Jim. Good call. Got that fixed. I was trying to cool my zone in the dead of winter. This is not very realistic for Toronto...for now!

New question to the group: Even on the coldest of days (~ -15C), my "Zone/Sys Sensible Cooling Rate [W](Hourly)" and "Fan Coil Sensible Cooling Rate[W]" are non-zero (and pretty high at 1-2 kW for a medium-sized zone), despite the fact that the chiller electrical load is 0W.  What's the meaning of  this? 

Thanks in advance,

Liam O'Brien

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes" <jim@...> wrote:
>
> Liam,
> 
> Essentially the same problem as " frost/freeze error", discussed earlier
> today
> 
>  
> 
> The Building Performance Team
> James V. Dirkes II, P.E., BEMP , LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
> 
>  
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Liam O'Brien
> Sent: Tuesday, March 20, 2012 12:51 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Air Cooled Condenser Inlet Temperature below
> 0C
> 
>  
> 
>   
> 
> Hi All,
> 
> I've got DOAS with Fan Coil units serving each zone. I'm getting this error
> message for many time steps during the year for my Toronto building:
> 
> ** Warning ** ElectricEIRChillerModel - CHILLER:ELECTRIC:EIR "MAIN CHILLER"
> - Air Cooled Condenser Inlet Temperature below 0C.
> 
> Any thoughts? 
> 
> Thanks,
> Liam
>



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/