Re: [EnergyPlus_Support] Re: Air Cooled Condenser Inlet Temperature below 0C



Your fan coil is using continuous fan operation and blowing cold air 
into the zone.

On 3/22/2012 10:46 AM, Liam O'Brien wrote:
> Thanks, Jim. Good call. Got that fixed. I was trying to cool my zone in the dead of winter. This is not very realistic for Toronto...for now!
>
> New question to the group: Even on the coldest of days (~ -15C), my "Zone/Sys Sensible Cooling Rate [W](Hourly)" and "Fan Coil Sensible Cooling Rate[W]" are non-zero (and pretty high at 1-2 kW for a medium-sized zone), despite the fact that the chiller electrical load is 0W.  What's the meaning of  this?
>
> Thanks in advance,
>
> Liam O'Brien
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes"<jim@...>  wrote:
>> Liam,
>>
>> Essentially the same problem as " frost/freeze error", discussed earlier
>> today
>>
>>
>>
>> The Building Performance Team
>> James V. Dirkes II, P.E., BEMP , LEED AP
>> 1631 Acacia Drive NW
>> Grand Rapids, MI 49504
>> 616 450 8653
>>
>>
>>
>> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
>> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Liam O'Brien
>> Sent: Tuesday, March 20, 2012 12:51 PM
>> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>> Subject: [EnergyPlus_Support] Air Cooled Condenser Inlet Temperature below
>> 0C
>>
>>
>>
>>
>>
>> Hi All,
>>
>> I've got DOAS with Fan Coil units serving each zone. I'm getting this error
>> message for many time steps during the year for my Toronto building:
>>
>> ** Warning ** ElectricEIRChillerModel - CHILLER:ELECTRIC:EIR "MAIN CHILLER"
>> - Air Cooled Condenser Inlet Temperature below 0C.
>>
>> Any thoughts?
>>
>> Thanks,
>> Liam
>>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/