[EnergyPlus_Support] Re: Air Cooled Condenser Inlet Temperature below 0C



Are you referring to outdoor air? I need the supply fan to run fairly continuously to supply outdoor air. And my cool water loop pump is off for the winter. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Your fan coil is using continuous fan operation and blowing cold air 
> into the zone.
> 
> On 3/22/2012 10:46 AM, Liam O'Brien wrote:
> > Thanks, Jim. Good call. Got that fixed. I was trying to cool my zone in the dead of winter. This is not very realistic for Toronto...for now!
> >
> > New question to the group: Even on the coldest of days (~ -15C), my "Zone/Sys Sensible Cooling Rate [W](Hourly)" and "Fan Coil Sensible Cooling Rate[W]" are non-zero (and pretty high at 1-2 kW for a medium-sized zone), despite the fact that the chiller electrical load is 0W.  What's the meaning of  this?
> >
> > Thanks in advance,
> >
> > Liam O'Brien
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes"<jim@>  wrote:
> >> Liam,
> >>
> >> Essentially the same problem as " frost/freeze error", discussed earlier
> >> today
> >>
> >>
> >>
> >> The Building Performance Team
> >> James V. Dirkes II, P.E., BEMP , LEED AP
> >> 1631 Acacia Drive NW
> >> Grand Rapids, MI 49504
> >> 616 450 8653
> >>
> >>
> >>
> >> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Liam O'Brien
> >> Sent: Tuesday, March 20, 2012 12:51 PM
> >> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >> Subject: [EnergyPlus_Support] Air Cooled Condenser Inlet Temperature below
> >> 0C
> >>
> >>
> >>
> >>
> >>
> >> Hi All,
> >>
> >> I've got DOAS with Fan Coil units serving each zone. I'm getting this error
> >> message for many time steps during the year for my Toronto building:
> >>
> >> ** Warning ** ElectricEIRChillerModel - CHILLER:ELECTRIC:EIR "MAIN CHILLER"
> >> - Air Cooled Condenser Inlet Temperature below 0C.
> >>
> >> Any thoughts?
> >>
> >> Thanks,
> >> Liam
> >>
> >
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/