Re: [EnergyPlus_Support] thermal mass





Alex,

As far as I know color of paint has very little effect on absorptivity/emissivity. According to the handbook rough concrete has e=0.94, while most of the paints regardless of color are in the range of 0.89 - 0.97. And white paint is white when it is sealed in the can. 
Polished aluminum or steel on the other hand may have e around 0.3 or even lower.          
I'm wandering if they sometimes wrap satellites or some parts of space hardware with high reflective foil having exactly the same as yours goal in their minds. 

Regarding thickness of concrete you may want to do some calculations because of  dynamic nature of your problem. Simple math model has time-dependent temperature penetration depth parameter that indicates a reduction of the effect of thickness on thermal inertia of the slab/wall. 

Pavel

On Mon, Mar 26, 2012 at 1:32 AM, regen555 <ap@xxxxxxxxx> wrote:
 

Dear all,

An off-topic question if you do not mind, suppose one has two (isolated/detached) rooms, Room A having hollow cement block walls 4 inches thick, Room B having same type of walls 10 inches thick. Rooms are free-running no ac's and all other parameters are identical. They have a 6 in. concrete roof. No insulation. Both rooms painted white all over.

The aim is to get the inside temperature as much as possible in tune with that outside since the rooms will house astronomical equipment and the movement of warm air currents from inside to the outside (or vice versa) will be of a disadvantage (during the night). Heat should be lost as rapidly as possible after sunset.

Which one of the rooms will provide the best solution? Logic would say that the one with the thicker walls provides more thermal mass and hence a reduction of the temperature swings inside the room. However, wouldn't the thicker walls (having more thermal inertia) absorb more heat throughout the day than the thinner ones and re-radiate this stored heat back during the night? A low thermal mass room on the other hand would cool down to ambient temp more rapidly.

Your views are appreciated.
Best regards,
Alex






__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___