There are many questions related to yours in the group mail.
If you read the I/O manual carefully, you will understand the purpose of each field in the designDay object.
In the .DDY file, there are many objects for Winter and Summer.
If you look at the title name, theres is a percentage value 0.4% 1%, .. 99.6%
The maximum drybulb temperature is taken from the weather file and compiled into statistics in the .STAT file.
The value of the max. dryBulb and the Wetbube at MD is used the third field, if WMD appears in the title. You can make up your own later on.
There is no Winter in Singapore. So I use four DesignDay data to represent four seasons to line up the solar agnle with the building, to study the heat through windows.
If you know the purpose of using the different ones, use as many as you want. The maximum and mininum values would be used for EPlus sizing, and they are listed in the fn-Zsz.csv fnSsz.csv files.
The best way to learn is to run a few 5zone example files.
I change the sky clearance, dates, day types, etc. to simulated different local conditions withing using the weather file.
Of course, the simulation is not exactly as using the annual weather file.
Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: homero.noboa@xxxxxxxxx Date: Tue, 27 Mar 2012 13:44:04 -0500 Subject: Re: [EnergyPlus_Support] Design Days
Hi Linda. Thanks for your prompt response.
Could you please tell us what happens when I include two summer design days in my model idf? Does E+ uses the worst? Uses the last? Is OK to include more than 1 design day per season?
Thanks. Homero.
On Tue, Mar 27, 2012 at 1:26 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
Homero Noboa, Ph. D. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |