Jim,
For a 100% Outdoor Air System (Proposed) the formula is:
Vot = Sum(Voz) 'Sum of the zone
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Vinay Devanathan
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jim Dirkes" <jim@...> wrote:
>
> Dear Curtis,
>
> I am not familiar with the report you mention. Where does it come from? And
> what does it measure?
>
> On the other hand, you seem to have answered at least part your own question
> by noting that minimums were identical for each of the two systems. Can you
> run a 62.1 compliance check? Or get it from the design engineer? To see if
> your minimum flows meet the 62.1 requirement?
>
>
>
> The Building Performance Team
> James V. Dirkes II, P.E., BEMP , LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of curtisjclark
> Sent: Tuesday, April 03, 2012 12:40 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Ventilation Requirements per ASHRAE 90.1
> Appendix G with a DOAS system
>
>
>
>
>
> Each zone is hardwired using DesignSpecification:OutdoorAir object using
> "Flow/Area" values.
>
> Curtis
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <vinay.devanathan@> wrote:
> >
> > You could hardwire the same OA cfm for each zone to what it is in the
> > design case.
> >> > On Tue, Apr 3, 2012 at 11:55 AM, curtisjclark <cjcfromslc@> wrote:
> >
> > > **
> > >
> > >
> > > We are using a DOAS system which delivers 100% outdoor air to the space.
> > > In the Baseline model (appendix G), it is a VAV system which delivers
> mixed
> > > outdoor air with return air.
> > >
> > > To meet the requirements of ASHRAE 62.1 in the Baseline model, I used
> the
> > > Ventilation Rate Procedure calculation method to determine the minimum
> > > outdoor air by using the Controller:MechanicalVentilation object with
> the
> > > same ventilation rates as in the DOAS system.
> > >
> > > The report for "Controller:OutdoorAir" shows the two system have same
> > > Minimum Outdoor Air Flow Rate. However, the report "Minimum Outdoor Air
> > > During Occupied Hours" shows a 84% reduction in outdoor air.
> > >
> > > Have I meet the requirements of Appendix G3.1.2.6 for ventilation?
> > >
> > >
> > >
> >
> >
> >
> > --
> > Vinay Dev
> >
>
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___