Dear Germán, EnergyPlus will automatically control the operation heating and cooling coil according to your SetpointManagers. It will not operate cooling and heating simultaneously unless you have some sort of CoolReheat control. (You can see this is you create output variables for the temperature node downstream of each coil) Regarding the frost warnings, you can: · Ignore the warnings (probably this does not affect accuracy too much, but you will get a lot of warnings!) · Create a two-speed DX coil (This will probably reduce the number of warnings) · Employ EMS to prevent DX coil operation below a certain outdoor temperature (e.g. 10-12C) The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of ecoeficientees Hi, I am stuck on the same problem. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.