Re: [EnergyPlus_Support] Ventilation System





ZoneMixing is one way -- as you describe.

ZoneCrossMixing would be the two way exchange between two zones.



At 04:01 AM 4/17/2012, Miroslav Bratanov wrote:


Thank you for the reply Linda!

I don't have air exchange between the zones, so I think zonemixing would not work for my case.
Probably I did not explain it properly in the first place, so I attached a simple scheme.

My system consists of:
Heat Exchanger
Heating Coil
Supply Fan
Exhaust Fan

The supply side of the system uses outside air which is processed in heat exchanger (primary flow) and heating coil and then fed to Zone 1 Science Labs.
The exhaust side of the system takes air from Zone 2 Bathrooms. The air goes through the heat exchanger (secondary flow) and then it is discharged to the outdoors.


On 16.04.2012 21:01, Linda Lawrie wrote:
 

Yes, the simplest form of this is called "zonemixing".

Example files that come with EnergyPlus include spreadsheets that illustrate where you can find each object.

At 11:59 AM 4/16/2012, Miroslav Bratanov wrote:
Dear EnergyPlus experts,

Is it possible to model a ventilation system in EPlus, which supplies
air to one zone and extracts the same amount of air from another zone?
Is there an example file for such case?

I have science labs zone and bathrooms zone. The ventilation system
supplies air to the science labs and extracts air from the bathrooms.
The science labs use separate exhaust ventilation system.

In other words the same system serves as a supply-only ventilation for
the science labs and exhaust-only ventilation for the bathrooms.

Thank you!
Miroslav



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
TODAY(Beta) ?






__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___