Good question. The temperature setpoint is applied to that node for that timestep to best reach the zone heating setpoint (in the case of using the multizone-heating setpoint manager, and the cooling setpoint in the case of using the cooling setpoint manager. The effect becomes apparent if you reference the setpoint on this node by your MixedAirSetpointManager which could for example be used to control your outdoor air mixing damper to best control the mixing to reach that setpoint. For example if your zone heating setpoint were 18 deg and the cooling setpoint were 26 deg, you may find using the multizone heating setpoint manager will give zone temps at around 18 deg, where as if you used the multizone cooling setpoint manager, they may pan out at 26 deg.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, ±è´ö¿ì <deukwookim@...> wrote:
>
> Dear Richard, 
> 
>  
> 
> Your suggestion is very helpful !
> 
> I used SetpointManager:Multizone:Heating object (due to multi-zones) at fan
> outlet air node of AHU, and the results shows that I really want it. 
> 
> The discharged air temperature was varied from 16 deg to 35 deg. according
> to the zone load profile.
> 
>  
> 
> 
> 
>  
> 
> Anyway, 
> 
>  
> 
> It was found that the capability of the SetpointManager:Multizone:Heating
> object also worked fine in summer design day. 
> 
> I don¡¯t know why E+ separate SetpointManager:Multizone:Heating and
> SetpointManager:Multizone:Cooling objects. 
> 
> Could you please let me know the differences? 
> 
>  
> 
> Best Regards, 
> 
> Deuk-Woo Kim
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/