Thanks for your response and sorry I didn't read your question correctly.
Exhaust fans are modeled as zone equipment fans similar to the ones in example file. When I looked at the hourly results, it make sense.The return flow from the zone is equal to the supply flow minus the exhaust flow and the same is true at the system level. However, the html report shows the same flow for both supply and return fans.> How have you modeled the exhaust fan?> thimmannaharshana@...> wrote:
>
> On Tue, May 1, 2012 at 10:45 AM, thimmannaharshana <
>
> > **> --
> >
> >
> > Hi all,
> >
> > I have modeled supply, return and exhaust fans for a system. when I look
> > at the results, the amount of airflow is same for both supply and return
> > fan. Energy plus is not accounting for the amount of exhaust flow while
> > calculating the return flow. The exhaust fan flow rate is reported
> > separately.
> >
> > Supply fan -6500 cfm
> > Return Fan -6500 cfm
> > Exhaust fan -550 cfm
> >
> > I am using energyplus for LEED submission and i guess this is a problem.
> >
> > Does any one know how to solve this and get the correct return airflow?
> >
> > Thanks in advance,
> > Harshana
> >
> >
> >
>
>
>
> Vinay Dev
>
--Vinay Dev
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___