[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Zone Exhaust and Return Fan



The return flow will equal the supply flow when the zone exhaust fans 
are off. Since the html file does not show every hour of the simulation, 
what exactly is that report telling you? The max flow rate?

On 5/1/2012 12:37 PM, thimmannaharshana wrote:
> Thanks for your response and sorry I didn't read your question correctly.
>
> Exhaust fans are modeled as zone equipment fans similar to the ones in example file. When I looked at the hourly results, it make sense.The return flow from the zone is equal to the supply flow minus the exhaust flow and the same is true at the system level. However, the html report shows the same flow for both supply and return fans.
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Vinay Devanathan<vinay.devanathan@...>  wrote:
>> How have you modeled the exhaust fan?
>>
>> On Tue, May 1, 2012 at 10:45 AM, thimmannaharshana<
>> thimmannaharshana@...>  wrote:
>>
>>> **
>>>
>>>
>>> Hi all,
>>>
>>> I have modeled supply, return and exhaust fans for a system. when I look
>>> at the results, the amount of airflow is same for both supply and return
>>> fan. Energy plus is not accounting for the amount of exhaust flow while
>>> calculating the return flow. The exhaust fan flow rate is reported
>>> separately.
>>>
>>> Supply fan -6500 cfm
>>> Return Fan -6500 cfm
>>> Exhaust fan -550 cfm
>>>
>>> I am using energyplus for LEED submission and i guess this is a problem.
>>>
>>> Does any one know how to solve this and get the correct return airflow?
>>>
>>> Thanks in advance,
>>> Harshana
>>>
>>>
>>>
>>
>>
>> -- 
>> Vinay Dev
>>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/