[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] OA controller and Heat Recovery
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] OA controller and Heat Recovery
- From: "thimmannaharshana" <thimmannaharshana@xxxxxxxxx>
- Date: Wed, 09 May 2012 19:09:17 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 09 May 2012 13:09:21 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1336590560; bh=JDOCvsVs48sHryG4JlEm/YEF+qKddNFnchyzoOKzj/8=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=RZ3hJI3JYRKnmXdNunoEnPTmN+1xKmmvk081+NBNmzSl7REK76nYzl82yGdVgVMHMukVoH8orG0wiWq7iD9EkDcGArL9/UKEeUGsoLSowNR5KYfVzE9raEodCZq5tq9u
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=Rsvk+T4Q20JObHCuqnShVc49qQZ73XvQLj8SEsZsJUJ/5MY6gOBD/9OscB67kNJ/PgsLd5tvQl/mivNzQP8ZXO4rtR0NIGTFoqJc9THOtFu4WPYVgn7FqphYbzkjZ9Xp;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Hi,
I am modeling heat recovery device for a VAV system. Based on the E+ documentation, input to the minimum OA air tab on OA controller has to be manually given(instead of auto-sizing) if the heat recovery device is modeled. I gave the minimum OA value and the file results in the below shown error. If I make the minimum OA input as zero then there are no errors. However, with 0 input in the minimum outdoor air tab the heat recovery device doesn't not recover any heat.
Does any of you know how to use heat recovery device in E+?
Thanks,
Harshana
** Severe ** FindRootSimpleController: Controller error for controller = "VAV SYSTEM 4 COOLING COIL CONTROLLER"
** ~~~ ** Environment=Burke Lakefront OH USA TMY3 WMO#=725245, at Simulation time=10/01 07:00 - 08:00
** ~~~ ** Controller function is inconsistent with user specified controller action = Reverse action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature set point = 11.60 [C]
** ~~~ ** Controller sensed temperature = 32.76 [C]
** ~~~ ** Controller actuator mass flow rate set to 17.65 [kg/s]
** ~~~ ** Controller actuator temperature = 6.74 [C]
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/