Jason,

Talk to me so I can learn something  …. I suspect that you have more experience interpreting 90.1, but it appears to me that you must use System 8 unless your facility is a lab (or any of the other exceptions).  If you have a lab with more than XXX outdoor air, then system type 5 or 7 becomes the baseline.

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jason Kirkpatrick
Sent: Tuesday, May 15, 2012 5:20 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] ASHRAE 90.1 Interpretation_LAB Building System Selection

 

 

Javed,

the rest of the paragraph is relevant:

For laboratory spaces with a minimum of 2400 L/sof
exhaust, use system type 5 or 7 that reduce the
exhaust and makeup air volume to 50% of design
values during unoccupied periods. For all-electric
buildings, the heating shall be electric resistance.

You mentioned the building size meant that you had to use system 8, so I must infer that you have an all electric building.
Therefore, you should use System 8 for the Lab.
Schedule the system flow rate (both supply and exhaust fans) to be at 100% of design flow during occupied periods and 50% of design during unoccupied periods.

Also note that G3.1.2.10 likely applies as well and the system will likely require energy recovery at 50% effectiveness.

Jason

On Tue,

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___