Homero, · Minimum OA set by DesignSpecification:OutdoorAir – good · No economizer – good · Large outdoor air amount to replace kitchen exhaust – good · I think that the error “Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze” only occurs when the coil is operating. You cannot suppress it (as far as I know). o That suggests that you may be mistaken about the coil being OFF during cold weather. Have you checked the Output:Variable value for “DX Coil Total Cooling Rate” of this coil? (It should be zero.) The
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.