[EnergyPlus_Support] Re: P or PI control
Thanks Phil
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Philip Haves <phaves@...> wrote:
>
> To clarify:
>
> There is no persistent offset in (proportional + integral (PI) control
> but there is a persistent offset in proportional-only (P) control. The
> effect of the integral action in a (well tuned) PI controller is to
> reduce the offset to zero on a timescale comparable to the response time
> of the plant. If this response time is short compared to the timescales
> of interest in the simulation, as it is for most HVAC loops (excluding
> zone temperature control and thermal storage tank control), then PI
> control is a very good approximation to the ideal control assumed in
> EnergyPlus.
>
> Phil
>
> On 5/20/2012 4:48 PM, Ooi wrote:
> >
> > This was explained last week. The time step integration among the
> > simulation managers is something better than PI, i believe. In PI
> > control, there will be an offset from the setpoint. EP Simulation does
> > not have these offset. It was explained that the offset depends on the
> > proportional band, which is very closely related to gain in the P.
> >
> > Hopw this helps.
> > ooi
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "ohchoen" <ohchoen@>
> > wrote:
> > >
> > > Hi, I'd like to know that it is possible P or PI Control using EP.
> > > is it possible??
> > >
> >
> >
>
> --
> Philip Haves
> Leader, Simulation Research Group
> Lawrence Berkeley National Laboratory
> One Cyclotron Road, MS 90R3111
> Berkeley, CA 94720-8134
> (510) 486 6512 (office)
> (510) 486 4089 (fax)
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/