Thank you Nick and Oscar.

On Fri, May 18, 2012 at 1:58 PM, Nick Caton <ncaton@xxxxxxxxxxxxxxxx> wrote:

Hi Vinay,

 

The key word here is ?predominant.? 

 

Carefully review the baseline system table footnotes, and also review the ?nonpredominant? exception regarding multiple baseline system types for applicability.  I?ve also experienced reviewers invoking the Table G3.1 requirement regarding ?where no heating exists use electric? into such decisions?  ?Predominant condition? is ultimately not a glossary term with a black & white definition,  so expect to define and substantiate/explain any decision you make.

 

There?s been much discussion around this issue for a variety of cases over the [equest-users] and [bldg-sim] mailing lists in the past.  Attached is one such discussion where I shared some related experience ? more like this discussion can be found in the archives ;).

 

Best of luck!

 

~Nick

cid:489575314@22072009-0ABB

 

NICK CATON, P.E.

SENIOR ENGINEER

 

Smith & Boucher Engineers

25501 west valley parkway, suite 200

olathe, ks 66061

direct 913.344.0036

fax 913.345.0617

www.smithboucher.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Oscar Dario
Sent: Friday, May 18, 2012 10:03 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Selecting the ASHRAE baseline

 

 


I think is PTAC because you are using fossil fuel for heating.

Sent from Yahoo! Mail on Android

 


From: Vinay Devanathan <vinay.devanathan@xxxxxxxxx>;
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>;
Subject: [EnergyPlus_Support] Selecting the ASHRAE baseline
Sent: Fri, May 18, 2012 2:49:27 PM

 

Hello,

 

I have a question about selecting the ASHRAE baseline system type -

 

For the proposed design I have a VRF system conditioning the building + DOAS system that tempering the OA and supplying it to the zones in the building. The DOAS has a DX Cooling Coil and a GAS heating coil.

 

So does this situation make my baseline a hybrid or Electric case? I want to know if it will be appropriate to choose PTHP or if I should be going with PTAC (it's a residential building).

 

All your thoughts will be greatly appreciated. Thanks in advance.

 

--

Vinay Dev




--
Vinay Dev



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___