Hold on, hold on.
No, I did not mean to say that I want to set the design day based on the weather of the weather file. I meant to say I want to set the DesignDay based on the Site.Location, that is defined in the Weather file.
If I want to run one simulation for several locations around the world, I have to define the DesignDay conditions appropriate to each location, just the way ASHRAE says we should and the way the DDY files do.
My problem, is that I want to **Automate** the definition of the design day with a macro, taking the ASHRAE DesignDay conditions according to the weather file I'm using in the simulation.
I would like my macro to say something like this:
##if Site = 55386 !Chicago. This comes from the weather file
DesingDay,MaxTemp = 38,
DesignDay,MaxDeltaT = 8,
##elseif Site = 78234 ! Mumbai. This comes from the weather file
DesignDay,MaxTemp = 46,
DesignDay,MaxDeltaT = 4,
....
##endif
Can this be done with an E+ macro? Can jEplus do this?
Thanks.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Dru Crawley <dbcrawley@...> wrote:
>
> The problem with using days from the weather files is that they often don't
> have anything as extreme as the long-term period of record design
> conditions published by ASHRAE. If you don't have design conditions, then
> the fallback could be using the data in the weather files. I have seen
> many weather files where the difference is 5 F or more -- which will
> radically affect auto-sizing.
>
> On Fri, Jun 1, 2012 at 5:51 PM, Jason Kirkpatrick <
> jason.alan.kirkpatrick@...> wrote:
>
> > **
> >
> >
> > I think it would be easier to just use the SizingPeriod:WeatherFileDays
> > object.
> >
> > Also, for the Site:Location object, this gets overridden by EnergyPlus if
> > it differs from the weather file anyway.
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/