Okay. you seem to be doing everything right. One point. The "design" air temperature is 14 deg and 33 repectively. This doesn't mean that the coil should always deliver this temp...only at "design conditions".

If your VAV damper is set to the minimum to achieve the required ODA, you may over-cool the zone. Better to use a SetpointManager:SingleZone<or multizone>cooling<and heating> objects to bound the max min temps but give the coils the flexibility to vary the cooling/heating outlet temps.

It will also help your coils to work together and avoid coil fighting.

Also (don't do this for ASHRAE as it is more work and you don't need to) bear in mind that usually a AHU has draw through configuration for the fan, and then you would incorporate the SetpointManager:MixedAir to incorporate the effects of fan heat addition to the airstream...if the coils are upstream, they see the heat addition and don't have to "look downstreem".

One last note for now...avoid slashes and special characters in names.
SetpointManager:Scheduled
Name Setpoint Manager/1



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/