Attached is a diagram showing what I meant by using the corner zones, etc. to illustrate the flow direction using the numbers in EPlus variables.
Dr. Li
Subject: Re: [EnergyPlus_Support] Re: Actual Air flow ?
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: vaibhav.energyarchitect@xxxxxxxxx
Date: Tue, 10 Jul 2012 21:19:10 +0200
Dear Dr.Li,The diagram is a graphical translation/representation of output variable: AirflowNetwork Mass Flow Rate from Node 1 to 2 (or node 2 to 1) as per I/O manual page no. 747, which is copied below. I used it to explain my colleagues in a simple/quick way about what this output variable means, hence shared here for others to see.AirflowNetwork Mass Flow Rate from Node 1 to 2 [kg/s]This is the AirflowNetwork linkage mass flow rate output in kg/s in the direction from Node 1to Node 2. It reports surface airflows through a crack or opening, and through linkagesdefined in an AirflowNetwork:Distribution:Linkage object. The surface linkage is divided intotwo types of surfaces, exterior surface and interior surface. Node 1 for an exterior surfacelinkage is a thermal zone and Node 2 is an external node. The value of AirflowNetwork MassFlow Rate from Node 1 to 2 represents the flow rate from a thermal zone to outdoors. Theflow direction through an interior surface crack or opening is defined from a thermal zonedefined by a surface?s Zone Name (Node 1) to an adjacent thermal zone defined by asurface?s OutsideFaceEnvironment (Node 2). For an AirflowNetwork:Distribution:Linkageobject, the value represents the air mass flow rate flowing from Node 1 to Node 2.Vaibhav Jain
On 10 July 2012 20:25, Lixing Gu <gu@xxxxxxxxxxxx> wrote:I would like to clarify what Lisa said in the last paragraph.
All incoming airflows are a part of zone loads, including infiltration,
ventilation and mixing. All outgoing airflows are not a part of zone loads.
Lixing------------------------------------
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of lisacng
Sent: Tuesday, July 03, 2012 9:36 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Actual Air flow ?
Alberto, Oscar
Just to make things clear, "inside" and "outside" aren't inside the building
and outside the building. It is the inside or outside face of the referenced
surface (AirflowNetwork:MultiZone:Surface // Surface name // Leakage
component name) where your leakage element is.
Also, in the same hour, you are seeing two different values for 1-->2 and
2-->1 in the same window because your time step is smaller than an hour. If
you output detailed or timestep results, you will see that only one flow
should have a value and the other is zero. The hourly output is an average
of the timestep outputs. If using the hourly results is fine, then the flow
of air is the difference of 1-->2 and 2-->1 and the direction is determined
by which is greater.
It should be noted that EnergyPlus only uses the flow into a building from
the outdoors to affect the load on a zone. Exfiltration (air leaving a
building) and mixing of air between zones does not affect load calculations.
Someone out there can correct me if I'm wrong.
Lisa Ng
NIST
IAQ & Ventilation Group
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, oscar hernandez
<oscarhernandez_81@...> wrote:
>
>
> Don't worry.
>
> If I remember, 1 to 2 is from outside to inside and 2 to 1 inside to
outside. Look at the energyplus input output manual (airflow network) you
have everything about that.
>
> Let me know if you need more help.
>
> Oscar.
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: ahneto@...
> Date: Sat, 30 Jun 2012 17:44:40 -0300
> Subject: RE: [EnergyPlus_Support] Actual Air flow ?
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Dear Oscar,
>
>
>
> Sorry to bother you again but , regarding the air flow network, how do
>
> I know the direction (from inside to outside and vice versa) of the
>
> flow in the window?
>
>
>
> Thanks for your help.
>
>
>
> Alberto
>
>
>
> Citando oscar hernandez <oscarhernandez_81@...>:
>
>
>
> >
>
> >
>
> > THe value 1 to 2 or 2 to 1 is the flow rate. You have to inside or
>
> > to outside.
>
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>
> > From: ahneto@...
>
> > Date: Fri, 29 Jun 2012 13:54:19 -0300
>
> > Subject: [EnergyPlus_Support] Actual Air flow ?
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> > Dear Forum,
>
> >
>
> >
>
> >
>
> > I modeling a room with the AirFlowNetwork object. I would like to
>
> >
>
> > confirm the following:
>
> >
>
> >
>
> >
>
> > When I set as output variable AirflowNetwork Mass Flow Rate from Node
>
> >
>
> > 1 to 2 and AirflowNetwork Mass Flow Rate from Node 2 to 1 for a
>
> >
>
> > exterior window, the difference between these two variables will give
>
> >
>
> > the actual flow rate and the direction will be set verifiying which
>
> >
>
> > variable is greater?
>
> >
>
> >
>
> >
>
> > Regards,
>
> >
>
> >
>
> >
>
> > Alberto Hernandez Neto
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
> >
>
Yahoo! Groups Links
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a
high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
__._,_.___