I think what Jason meant is that if the zone being served by the facade (and not the facade zone itself) is occupied, you should model it as an independent zone, together with airflow network.
There is some literature about the covection coefficients in a DSF, but E+ doesn't have an algorithm that applies directly to this case. From the comparisons that I've made, the ISO15099Windows, found in the adaptive convection algorithm, seems to be the one that better aproximates some of the propososed models for the inside convection.
Pedro.
On 31-05-2012 8:02, Denis Piccoli wrote:Thank you Jason
Actually my Double skin facade is a box window but to simplify the simulation I modeled it as a corridor facade.The cavity is not a occupiable space, it is only 110 mm wide.In this case I think that the best thing is to model with WindowProperty:AirflowControl
2012/5/30 Jason Kirkpatrick <jason.alan.kirkpatrick@xxxxxxxxx>
If your double wall cavity is truly a corridor and is occupiable space included in ventilation calculations and having its own air terminals, then you will want it to be modeled as its own thermal zone.
If this is not occupiable space, you may be making the model unnecessarily complex by modeling the cavity as a separate zone.
I would suggest looking into the WindowProperty:AirflowControl & WindowProperty:ShadingControl to see if the options shown there represent your cavity airflow and shading. If yes then you could just model as a wall with a construction with 1.1 m air gap.
If you do end up with the cavity having its own thermal zone, and you want to pass light through this thermal zone to model daylighting sensors on the interior, you will need to model all thermal zones as convex. A formal definition of convex is that any straight line passing through the zone intercepts at most two surfaces.
Hope this helps.
Jason
This email and any files enclosed, contain confidential business information for use only by the addressed, please note that, in accordance with Permasteelisa Group Policy, the company could read them. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the Company. If you have received this email in error, please delete it from your system. Any use or distribution of the contents of this email by a not-intended recipient or in violation of the purposes of this email is strictly prohibited and could be unlawful. Permasteelisa Group accepts no liability for any damage caused by any virus, worm, trojan program or any other malicious program transmitted by this email.
This email and any files enclosed, contain confidential business information for use only by the addressed, please note that, in accordance with Permasteelisa Group Policy, the company could read them. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the Company. If you have received this email in error, please delete it from your system. Any use or distribution of the contents of this email by a not-intended recipient or in violation of the purposes of this email is strictly prohibited and could be unlawful. Permasteelisa Group accepts no liability for any damage caused by any virus, worm, trojan program or any other malicious program transmitted by this email.
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___