[EnergyPlus_Support] Re: Error explanation needed



Hello,
I got the following warning:

** Warning ** WriteVeriSumTable: InputVerificationsAndResultsSummary: Wall area based on [>=60,<=120] degrees (tilt) as walls
   **   ~~~   ** differs ~5.9% from user entered Wall class surfaces. Degree calculation based on ASHRAE 90.1 wall definitions.
   **   ~~~   ** Calculated based on degrees=[2604.855] m2, Calculated from user entered Wall class surfaces=[2460.135] m2.
   **   ~~~   ** Check classes of surfaces and tilts for discrepancies.

All the walls of my model should be vertical.
Is all the relative information available in the .eio file? I checked there but all the walls seem to have an inclination of 90 degree. Actually, the walls are a lot. Perhaps I didn't see the walls that are not considered vertical. What is the quickest way to see which surfaces generate the warning?
Best Regards
Francesco Passerini


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Miroslav Bratanov <miroslav_bratanov@...> wrote:
>
> Hello Everybody,
> 
> Where can I find more information on the following error:
> 
> ** Warning ** WriteVeriSumTable: InputVerificationsAndResultsSummary: 
> Wall area based on [>=60,<=120] degrees (tilt) as walls
>     **   ~~~   ** differs ~17.6% from user entered Wall class surfaces. 
> Degree calculation based on ASHRAE 90.1 wall definitions.
>     **   ~~~   ** Calculated based on degrees=[5167.071] m2, Calculated 
> from user entered Wall class surfaces=[4393.927] m2.
>     **   ~~~   ** Check classes of surfaces and tilts for discrepancies.
> 
> The building that I model has inclined roofs which I think are causing 
> this. But the incline of the roof surfaces is less than 20 degrees, so 
> they shouldn't be considered as walls judging by "Wall area based on 
> [>=60,<=120] degrees (tilt) as walls".
> 
> I searched the documentation but did not find anything on this topic.
> Any help is appreciated!
> 
> Thank you!
> Miroslav
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/