You have a two pipe fan coil unit in each zone. This is a zone unit, and does not need an AHU. The OA mixer may be included in the unit.
You need two water plants, one for HW and one for ChW. EPlus does not switch plant loops, so you will connect them as a four pipe system. In Summer, the chiller is turned on. In Winter the boiler is turned on. The change over days are assigned by you with a schedule. How much energy are wasting? I think, you are referring to the days that the system is on and the fan coil units are not running. In Eplus, the plant would be turned off when there is no demand. EPlus does not simulate pipe loss (all specified as adiabatic). The tank, if used, may have a conduction loss to the environment. Therefore the annual simulation would not give you the idle energy wasting values. In a real system, you will observe the PLR when idle, and use that to estimate the energy usage. For example the chiller may cycle between 12.5 and 7.5°C. Start at 12.5°C run till the water is at 7.5°C and then turn off. The energy wastage is entirely on the tank and pipes, and the power is for the pump and the fan at the EIR. These cannot be easily simulated, because the location and environment for these pipes are not known. You may simulate the effect with an equivalent storage tank. The plant will keep this tank at the designed water loop temperature when the demand is zero. The direct answer to you question on the EPlus template usage is that the set of templates must be for the appropriate application.. You will use the HVACtemplate:Zone: for the fan coil unit. and the HVACtemplate:plant for the water plant, boiler and chiller. VAV for the zone is an adjustable damper for an air duct, which is to be used with a HVACtemplate:system. (two templates) to form the DOAS (AHU system). An additional fan coil unit in the zone is still possible, but not easy to specify, because one zone thermostat cannot control two sets of equipment.. You can only specify one HVACtemplate:Thermostat for each zone. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: matthew.sverre.anderson@xxxxxxxxx Date: Tue, 7 Aug 2012 22:04:32 +0000 Subject: [EnergyPlus_Support] Multiple HVACTemplates Per Zone Error
Hey Everybody,
So I have a system that has central handlers feeding 5 zones, 1 basement, 2 north/south for the 1st and 2nd floor. It then has a room fancoil system that heat/cools the same zones. The fancoil system is two pipe with a switch over where we can only heat or cool at any given time. I would like to get to the point where I can correctly model the amount of energy we are wasting in switch overs, I have done this in excel already but I would like to figure this out in E+. In trying to put both a fan coil and a VAV air handler into a zone I received an error regarding the DSOA systems where it is trying to tell me I can't have more than one HVAC Template per system. Is this true? Any work arounds here? __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |