Francesco, Comments interspersed below James V Dirkes II, PE, BEMP, LEED AP The Building Performance Team Inc 1631 Acacia Drive, Grand Rapids, MI 49504 616 450 8653 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of FrancescoP I have some doubts concerning the sizing of baseline equipment according to APPENDIX G of ASHRAE 90.1. This is correct. E+ performs sizing coincident with simulation. If you elect to make a separate “sizing” run, the same criteria, including “Autosize”, must be used for both.
This object does not affect sizing at all. The criteria that E+ uses are contained in the Sizing:System and Sizing:Zone objects.
The Baseline model must use the power adjustments consistent with the Proposed model. E.g., if the Proposed model is fully ducted, the Baseline fan power should include that adjustment. p.s., I am guessing that “WC” is a “water closet”, but I am not sure ….
The rooms which have mechanical extract systems should be modeled as having a Fan:ZoneExhaust. The pressure adjustments do not normally apply to these. (A pressure adjustment would apply to something like a laboratory extract system which has mechanized dampers for flow control.)
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |