RE: [EnergyPlus_Support] Cycling fans when spaces are unoccupied





Carolina,

Consider using the AvailabilityManager:NightCycle.  If you specify constant fan operation during occupied hours, this manager will cycle the fan as needed during unoccupied hours.

 

James V Dirkes II, PE, BEMP, LEED AP

The Building Performance Team Inc

1631 Acacia Drive, Grand Rapids, MI 49504

616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Carolina Galeazzi
Sent: Thursday, August 16, 2012 10:51 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Cycling fans when spaces are unoccupied

 

 

Hi Richard,

Thank you for your answer.

So, the correct values for cycling fans in the fan operation mode schedule is:

 

0 (denotes cycling fan operation), used in unoccupied hours;

1 or other value other than 0 (denote continuos fan operation), specified for occupied hours.

 

Is this correct?

Carol

 

De: Richard Raustad <RRaustad@xxxxxxxxxxxx>
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Enviadas: Quinta-feira, 16 de Agosto de 2012 11:26
Assunto: Re: [EnergyPlus_Support] Cycling fans when spaces are unoccupied

 

 

Just because you don't need to be bring OA in at night doesn't mean that you don't need to condition the zones, which means the supply fan must turn on.
During the day, the fan runs continuously to ensure the proper amount of OA, during the night, if there is a load, the fan turns on and off with the coils.

There is usually a fan operating mode schedule used with HVAC equipment that can cycle, or you can use a night ventilation manager to cycle the fan on for VAV systems.
OA control is independent of fan operation (i.e., you can have OA or not if the fan is running).

On 8/16/2012 10:12 AM, Carolina Galeazzi wrote:

Hi All,

 

To build an ASHRAE baseline model, it's said that 'supply and return fans should be cycled to meet heating and cooling loads during unoccupied hours'. I understand that fans should run for mechanical ventilation, but with zero outside airflow rate. How can I cycle the variable volume fan of the AHUs in Eplus, with zero outside airflow rate?

Thank you for your help!!

Carol

 

  

 

 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu/
 
UCF - From Promise to Prominence: Celebrating 40 Years

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___