I agree. I may be wrong. Therefore I explained the operation in detail, as I did the tests.
I mentioned that whether the HVACtemplate:zone is now using the set point manager mode in the zone VAV. I have not seen a setpoint manager example in Version 7 which links the reheat heater to the VAV damper position. I have tested the version 6 operation with different VAV supply air temperature and damper postion. If you are using the setpoint manager:reheat, I would expect problems. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Tue, 21 Aug 2012 12:47:23 -0500 Subject: RE: [EnergyPlus_Support] Cooling follows heating setpoint I recommend testing it to see what happens. (but that?s what it does for me every time.) Also, see Richard Raustad?s post on 8/17 regarding this topic.
James V Dirkes II, PE, BEMP, LEED AP Energy Analysis, Commissioning & Training Services
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of YuanLu Li
I do not think this is always true. The reheat heater has two functions. For cooling it is a reheat heater, which follows the cooling setpoint schedule. For heating, it is the zone main heater which follows the heat set point schedule. To: EnergyPlus_Support@xxxxxxxxxxxxxxx EnergyPlus maintains the heating setpoint during cooling season for reheat systems
James V Dirkes II, PE, BEMP, LEED AP Energy Analysis, Commissioning & Training Services
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of bhensii
I have a VAV system in a building.
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.