Re: [EnergyPlus_Support] the predictor-corrector procedure in the engineering manual of Energy Plus





I may not be the most qualified to discuss this, but I'll give some thoughts:

Yes, I think you are on the right track for how the predictor-corrector operates at a high-level.  As for the initialization at 23 degrees, that only happens very early in the simulation, and the dependence on this initial condition is reduced through the warm-up procedure.  As for not hitting set-point, the system simply may not be able to meet the set-point at any given time.  The result is that the zone temperature floats. 

Edwin

On Wed, Aug 22, 2012 at 4:24 PM, bokelai1989 <bokelai1989@xxxxxxxxx> wrote:
 

Hi, all,
I am learning the energy plus calculation mechanism.

The predictor-corrector scheme can be summarized as follows:
? Using equation (6), an estimate is made of the air system energy required to balance
the equation with the zone air temperature equal to the setpoint temperature.
? With that quantity as a demand, the air system is simulated to determine its actual
supply capability at the time of the simulation. This will include a plant simulation if
necessary.
? The actual air system capability is used in equation (14) to calculate the resulting
zone temperature.

Could any one give more specific explanation about this whole process? I am very confused about how it deals with the temperatures. So it first starts with initializing all the temperatures at 23C, and then through iteration to obtain the estimated system energy, and then an actual system energy, then an updated temperature, which if not reach the setpoint temp, then continue to do an iteration?

Thanks so much!
Best,
Na




--
Edwin Lee
Doctoral Candidate, Oklahoma State University
ASHRAE Student Member, Former ASHRAE OSU Student Branch President
Office: ATRC 303: 405-744-3727



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___