[EnergyPlus_Support] plantloop fluid temperature too low
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] plantloop fluid temperature too low
- From: "shubou" <dingwenting@xxxxxxxxx>
- Date: Fri, 24 Aug 2012 09:32:01 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 24 Aug 2012 03:32:06 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1345800725; bh=4b6SeHHas/vO4Wx+HKar6i6ApOkPr0URQw0YP65Lax0=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=opeyBL6ssc0nBxt+qF1WcJlK+mxDxsbzgo+uPsS6lYu+vC1JiBQvtXtQV40G2ENyhlZ/IvdN+xSE6Mplv+rkRrxtrQHsGQxmid+PzrlIDVQDjdd4Eb+BHKpoEDBczfvI
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=dmoMokxeXni++RN4TuJlWmyft7+MAOuJspjjWFX7xnmP1siG9d+czwllwXR1ffX5uImDNaZKDn9CRYdIMg322gfFcI5i2geaK8cMw3SKyyfRXhqpu6z3aA0i6kvMbQDn;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
who can tell me how to solve the following problem?
I use outdoorunit+radiant floor for every air-conditioned zone and the plant is water to water heat pump.
The error is
Plant temperatures are getting far too cold, check controls and relative loads and capacities
** ~~~ ** Environment=TOKYO HYAKURI - JPN IWEC Data WMO#=477150, at Simulation time=05/01 13:05 - 13:10
** ~~~ ** PlantLoop Name (SupplySide)= COOLSYS1
** ~~~ ** PlantLoop Setpoint Temperature=6.7 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) "COOLSYS1 SUPPLY OUTLET NODE" has temperature=-484.6 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) "COOLSYS1 SUPPLY INLET NODE" has temperature=7.4 {C}
** ~~~ ** PlantLoop Minimum Temperature=1.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=98.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=0.0 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=0.5 {kg/s}
** ~~~ ** PlantLoop Node (SupplySide) "COOLSYS1 SUPPLY OUTLET NODE" has mass flow rate =0.5 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=126.4 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Cooling Demand=1683.1 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=1138411.7 {W}
** ~~~ ** PlantLoop Capacity=1800000.0 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=1800000.0 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=COOLSYS1 LOOP OPERATION SCHEME LIST
** ~~~ ** PlantLoop Operation Dispatched Load = 1683.1 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 1683.1 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
** ~~~ ** Branches on the Loop.
** ~~~ ** Demand Branches:
** ~~~ ** COOLSYS1 DEMAND INLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:COOLSYS1 DEMAND INLET PIPE
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 1
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:PW RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 2
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:INT RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 3
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:PW-MID RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 4
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:INT-MID RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 5
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:PW-TOP RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 6
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW:INT-TOP RADIANT FLOOR
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 7
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:PWCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 8
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:INTCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 9
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:PW-MIDCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 10
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:INT-MIDCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 11
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:PW-TOPCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND LOAD BRANCH 12
** ~~~ ** Components on Branch:
** ~~~ ** COIL:COOLING:WATER:INT-TOPCOOLINGCOIL
** ~~~ ** COOLSYS1 DEMAND BYPASS BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:COOLSYS1 DEMAND BYPASS PIPE
** ~~~ ** COOLSYS1 DEMAND OUTLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:COOLSYS1 DEMAND OUTLET PIPE
** ~~~ ** Supply Branches:
** ~~~ ** COOLSYS1 SUPPLY INLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PUMP:VARIABLESPEED:COOLSYS1 PUMP
** ~~~ ** COOLSYS1 SUPPLY EQUIPMENT BRANCH 1
** ~~~ ** Components on Branch:
** ~~~ ** HEATPUMP:WATERTOWATER:EQUATIONFIT:COOLING:GSHPCLG1
** ~~~ ** COOLSYS1 SUPPLY EQUIPMENT BRANCH 2
** ~~~ ** Components on Branch:
** ~~~ ** HEATPUMP:WATERTOWATER:EQUATIONFIT:COOLING:GSHPCLG2
** ~~~ ** COOLSYS1 SUPPLY EQUIPMENT BYPASS BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:COOLSYS1 SUPPLY EQUIPMENT BYPASS PIPE
** ~~~ ** COOLSYS1 SUPPLY OUTLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:COOLSYS1 SUPPLY OUTLET PIPE
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/