Jeremiah,The problem is not because of your window. Window coordinates are fine:FenestrationSurface:Detailed,Block1:Zone1_Wall_5_0_0_0_0_0_Win, !- NameWindow, !- Surface TypeWindow, !- Construction NameBlock1:Zone1_Wall_5_0_0, !- Building Surface Name, !- Outside Boundary Condition Object0.5, !- View Factor to GroundWindow Shade Control, !- Shading Control NameFrame & Divider , !- Frame and Divider Name1, !- Multiplier4, !- Number of Vertices-3.74464827, !- Vertex 1 X-coordinate {m}-3.637644475, !- Vertex 1 Y-coordinate {m}0.97536, !- Vertex 1 Z-coordinate {m}-1.30983827, !- Vertex 2 X-coordinate {m}-3.637644475, !- Vertex 2 Y-coordinate {m}0.97536, !- Vertex 2 Z-coordinate {m}-1.30983827, !- Vertex 3 X-coordinate {m}-3.637644475, !- Vertex 3 Y-coordinate {m}1.9812, !- Vertex 3 Z-coordinate {m}-3.74464827, !- Vertex 4 X-coordinate {m}-3.637644475, !- Vertex 4 Y-coordinate {m}1.9812; !- Vertex 4 Z-coordinate {m}Your shading cause the problem. the extension from the window is 0 for left and right. If you read the error again it is about surface="FIN Left". Fix the lines below. start at line 2286 in your file.!- =========== ALL OBJECTS IN CLASS: SHADING:FIN:PROJECTION ===========Shading:Fin:Projection,Fin, !- NameBlock1:Zone1_Wall_5_0_0_0_0_0_Win, !- Window or Door Name0, !- Left Extension from Window/Door {m}0, !- Left Distance Above Top of Window {m}0, !- Left Distance Below Bottom of Window {m}90, !- Left Tilt Angle from Window/Door {deg}0.0001, !- Left Depth as Fraction of Window/Door Width {m}0, !- Right Extension from Window/Door {m}0, !- Right Distance Above Top of Window {m}0, !- Right Distance Below Bottom of Window {m}90, !- Right Tilt Angle from Window/Door {deg}0.0001; !- Right Depth as Fraction of Window/Door Width {m}MostaphaOn Thu, Aug 30, 2012 at 7:14 PM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:
But I want to use a blind with glare shading control and the window is operable with air flow network- will "window" work for this?
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
On Thu, Aug 30, 2012 at 5:13 PM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:
Thanks Linda I will give that a shot.
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
On Thu, Aug 30, 2012 at 5:05 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:There are two "simple" window objects that you might use.
Window and
WIndow:Interzone
you define the window by length and height - relative to the surface
origin on which it sits.> JEREMIAH D. CROSSETT | Senior Analyst | Phase Change Energy
On 2012-08-30 18:02, Jeremiah Crossett wrote:
> Mostpha,
> Attached is my base file I have used this change out building
> surfaces
> and window before without a problem- today I am using it for a dorm
> and it is having this issue- titled Dorm-r-shoebox, and
> the geometry file that I got the window from titled geometry-2.
>
> Narij- I am not sure how to define a window correctly by number in
> idf
> editor? possibly you could let me know how you advise I do so? or are
> you saying to do it in open studio?
>
> Solutions
> 120 E. PRITCHARD ST. | ASHEBORO, NC 27203 | MOBILE 503-688-8951> [15]> wrote:
>
>>
>>
>> Jeremiah,
>>
>> At this point I would also, just for the sake of it, try defining
>> the window directly into the .idf file as opposed to copying it from
>> DB into Eplus, and running it? Unless, the DB produced a .idf file
>> and you copied the object from the .idf file. I have not worked
>> across the DB and Eplus platforms so I do not know the work flow
>> between the two.
>>
>> Niraj
>>
>> On Thu, Aug 30, 2012 at 7:41 PM, Jeremiah Crossett>> <jcrossett@xxxxxxxxxxxxxxx [14]> wrote:>>> JEREMIAH D. CROSSETT | Senior Analyst | Phase Change
>>
>>>
>>>
>>> Any further advise would be great- it just does not make since to
>>> see a window in place but have it not run- I deleted the daylight
>>> sensor and still having the issue.
>>>
>>> Energy Solutions
>>> 120 E. PRITCHARD ST. | ASHEBORO, NC 27203 | MOBILE
>>>
>>>
>>>
>>>
>>>
>>> On Thu, Aug 30, 2012 at 4:37 PM, Jeremiah Crossett>>> <jcrossett@xxxxxxxxxxxxxxx [13]> wrote:>>>> JEREMIAH D. CROSSETT | Senior Analyst | Phase Change
>>>
>>>> Niraj, Linda, Ned
>>>>
>>>> So I opened my file in open studio to see if there was a window
>>>> there (before I started trying to understand how
>>>> the vertices related to each other and found that the daylight
>>>> sensor was outside of the space, and that the window was in the
>>>> right place....
>>>>
>>>> The strange thing is now I try to change where the daylight
>>>> sensor is located but that does not fix the issue-
>>>>
>>>> Energy Solutions
>>>> 120 E. PRITCHARD ST. | ASHEBORO, NC 27203 | MOBILE
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Thu, Aug 30, 2012 at 4:25 PM, Jeremiah Crossett>>>> <jcrossett@xxxxxxxxxxxxxxx [12]> wrote:>>>>> JEREMIAH D. CROSSETT | Senior Analyst | Phase Change
>>>>
>>>>> I just came across that- and it is "relative" for both the
>>>>> source file I took the window from and the file I am trying to
>>>>> use it within.
>>>>>
>>>>> Energy Solutions
>>>>> 120 E. PRITCHARD ST. | ASHEBORO, NC 27203 | MOBILE
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Thu, Aug 30, 2012 at 4:21 PM, Niraj Poudel>>>>> <nirajpdl@xxxxxxxxx [11]> wrote:
>>>>>
>>>>>>
>>>>>>
>>>>>> Jeremiah,
>>>>>>
>>>>>> Do you have your "rectangular surface coordinate system" in
>>>>>> the GlobalGeometryRules object defined in the "relative" or
>>>>>> the "absolute" co-ordinate system?
>>>>>> I think that is what Linda is alluding to. I might be
>>>>>> wrong.
>>>>>>
>>>>>> Niraj
>>>>>>
>>>>>> On Thu, Aug 30, 2012 at 7:13 PM, Jeremiah Crossett>>>>>> <jcrossett@xxxxxxxxxxxxxxx [10]> wrote:>>>>>>> JEREMIAH D. CROSSETT | Senior Analyst | Phase
>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> Sorry to be "dumb" but I do not quite understand the
>>>>>>> question- do you mean relative to the building surface
>>>>>>> detailed?
>>>>>>>
>>>>>>> Change Energy Solutions
>>>>>>> 120 E. PRITCHARD ST. | ASHEBORO, NC 27203 | MOBILE
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> On Thu, Aug 30, 2012 at 3:54 PM, Linda Lawrie>>>>>>>>> Mobile 503-688-8951 [1]>>>>>>> <linda@xxxxxxxxxxxxxx [9]> wrote:
>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> Do you have relative coordinates? Such that when
>>>>>>>> turned to "absolute" you have this?
>>>>>>>>
>>>>>>>> At 04:38 PM 8/30/2012, Jeremiah Crossett wrote:
>>>>>>>>
>>>>>>>>> Ned & Linda-
>>>>>>>>> Thank you for your avise- Now I am not sure what
>>>>>>>>> approach to take as the funny thing is that the
>>>>>>>>> origonal db file did not have any issue with this
>>>>>>>>> window:
>>>>>>>>>
>>>>>>>>> NameBlock1:Zone1_Wall_5_0_0_0_0_0_Win
>>>>>>>>> Surface TypeWindow
>>>>>>>>> Construction Name1001
>>>>>>>>> Building Surface NameBlock1:Zone1_Wall_5_0_0
>>>>>>>>>
>>>>>>>>> Outside Boundary Condition Object
>>>>>>>>>
>>>>>>>>> View Factor to Ground.5
>>>>>>>>> Shading Control Name1001
>>>>>>>>> Frame and Divider Name1
>>>>>>>>> Multiplier1
>>>>>>>>> Number of Vertices4
>>>>>>>>> Vertex 1 X-coordinate-3.74464827
>>>>>>>>> Vertex 1 Y-coordinate-3.637644475
>>>>>>>>> Vertex 1 Z-coordinate.97536
>>>>>>>>> Vertex 2 X-coordinate-1.30983827
>>>>>>>>> Vertex 2 Y-coordinate-3.637644475
>>>>>>>>> Vertex 2 Z-coordinate.97536
>>>>>>>>> Vertex 3 X-coordinate-1.30983827
>>>>>>>>> Vertex 3 Y-coordinate-3.637644475
>>>>>>>>> Vertex 3 Z-coordinate1.9812
>>>>>>>>> Vertex 4 X-coordinate-3.74464827
>>>>>>>>> Vertex 4 Y-coordinate-3.637644475
>>>>>>>>> Vertex 4 Z-coordinate1.9812
>>>>>>>>>
>>>>>>>>> Jeremiah D. Crossett | Senior Analyst | Phase
>>>>>>>>> Change Energy Solutions
>>>>>>>>>
>>>>>>>>> 120 E. Pritchard St. | Asheboro, NC 27203 |
>>>>>>>>>
>>>>>>>>> www.phasechange.com [2]
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> On Thu, Aug 30, 2012 at 3:13 PM, Jeremiah Crossett <>>>>>>>>> jcrossett@xxxxxxxxxxxxxxx [3]> wrote:>>>>>>>>> Mobile 503-688-8951 [4]
>>>>>>>>>
>>>>>>>>> I found the issue, I pasted a window in place from a
>>>>>>>>> DB file, and it was rejected- BUT I can not understand
>>>>>>>>> why? the vertices's look like they are in the right
>>>>>>>>> place-and I want the change the window like I have
>>>>>>>>> many times before... Any advise?
>>>>>>>>>
>>>>>>>>> Jeremiah D. Crossett | Senior Analyst | Phase
>>>>>>>>> Change Energy Solutions
>>>>>>>>> 120 E. Pritchard St. | Asheboro, NC 27203 |
>>>>>>>>
>>>>>>>> www.phasechange.com [5]
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> On Thu, Aug 30, 2012 at 3:06 PM, Jeremiah Crossett <>>>>>>>> 503-688-8951 [7]>>>>>>>> jcrossett@xxxxxxxxxxxxxxx [6]> wrote:
>>>>>>>>
>>>>>>>> Anyone have ideas for this one> it was working fine and
>>>>>>>> I changed an airflow setting then this> when I change
>>>>>>>> back it does not go away...?
>>>>>>>>
>>>>>>>> Program Version,EnergyPlus-64-MP 7.1.0.012, 8/30/2012
>>>>>>>> 3:03 PM,IDD_Version 7.1.0.012
>>>>>>>> ************* Beginning Zone Sizing Calculations
>>>>>>>> ** Severe ** CalcCoordinateTransformation:
>>>>>>>> Invalid dot product, surface="FIN Left":
>>>>>>>> ** ~~~ ** ( -3.745, -3.638,
>>>>>>>> 1.981)
>>>>>>>> ** ~~~ ** ( -3.745, -3.638,
>>>>>>>> 0.975)
>>>>>>>> ** ~~~ ** ( -3.745, -3.638,
>>>>>>>> 0.975)
>>>>>>>> ** ~~~ ** ( -3.745, -3.638,
>>>>>>>> 1.981)
>>>>>>>> ** Fatal ** CalcCoordinateTransformation:
>>>>>>>> Program terminates due to preceding condition.
>>>>>>>> ...Summary of Errors that led to program
>>>>>>>> termination:
>>>>>>>> ..... Reference severe error count=1
>>>>>>>> ..... Last severe
>>>>>>>> error=CalcCoordinateTransformation: Invalid dot product,
>>>>>>>> surface="FIN Left":
>>>>>>>> ************* Warning: Node connection errors
>>>>>>>> not checked - most system input has not been read (see
>>>>>>>> previous warning).
>>>>>>>> ************* Fatal error -- final processing.
>>>>>>>> Program exited before simulations began. See previous
>>>>>>>> error messages.
>>>>>>>> ************* EnergyPlus Warmup Error Summary.
>>>>>>>> During Warmup: 0 Warning; 0 Severe Errors.
>>>>>>>> ************* EnergyPlus Sizing Error Summary.
>>>>>>>> During Sizing: 0 Warning; 1 Severe Errors.
>>>>>>>> ************* EnergyPlus Terminated--Fatal Error
>>>>>>>> Detected. 0 Warning; 1 Severe Errors; Elapsed Time=00hr
>>>>>>>> 00min 0.86sec
>>>>>>>>
>>>>>>>> Jeremiah D. Crossett | Senior Analyst | Phase
>>>>>>>> Change Energy Solutions
>>>>>>>> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile
>>>>>>>> www.phasechange.com [8]> Links:
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>
>>>>>> --
>>>>>>
>>>>>> Niraj Poudel, Architectural Engineer.
>>>>>> PhD student, PDBE Program.
>>>>>> Clemson University, Clemson, SC.
>>
>> --
>>
>> Niraj Poudel, Architectural Engineer.
>> PhD student, PDBE Program.
>> Clemson University, Clemson, SC.
>
>
>
> ------
> [1] http://mail.fortlawrie.com/tel:503-688-8951
> [2] http://www.phasechange.com
> [3] mailto:jcrossett@xxxxxxxxxxxxxxx
> [4] http://mail.fortlawrie.com/tel:503-688-8951
> [5] http://www.phasechange.com
> [6] mailto:jcrossett@xxxxxxxxxxxxxxx
> [7] http://mail.fortlawrie.com/tel:503-688-8951
> [8] http://www.phasechange.com
> [9] mailto:linda@xxxxxxxxxxxxxx
> [10] mailto:jcrossett@xxxxxxxxxxxxxxx
> [11] mailto:nirajpdl@xxxxxxxxx
> [12] mailto:jcrossett@xxxxxxxxxxxxxxx
> [13] mailto:jcrossett@xxxxxxxxxxxxxxx
> [14] mailto:jcrossett@xxxxxxxxxxxxxxx
> [15] mailto:nirajpdl@xxxxxxxxx
> [16] http://energyplus.helpserve.com
> [17] http://www.energyplus.gov
> [18] http://groups.yahoo.com/group/EnergyPlus_Support/
> [19]
>
> http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmazgzYzZtBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNDYzNzEzODE-
> [20]
>
> mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=EmailDelivery:Digest
> [21]
>
> http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkaThib2J2BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzQ2MzcxMzgx
> [22] http://docs.yahoo.com/info/terms/
> [23]
>
> mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe