From: Linda Lawrie <linda@xxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, September 24, 2012 10:46 AM
Subject: Re: [EnergyPlus_Support] (unknown)
I am trying to convert idf files
from 6.0 to 7.0. Can you help me understand what I may need
to do to fix the problem below.
Thanks,
Carla
Conversion 6.0 => 7.0
Starting new Transition.audit
** Fatal ** Energy+.idd missing. Program
terminates. Fullname=V6-0-0-Energy+.idd
Conversion 7.0 => 7.1
Starting new Transition.audit
Will create new full IDFs
Will create new IDF lines with units where applicable
Will create new IDF lines leaving blank incoming fields as blank
(no default fill)
Processing IDF --
C:\NILM_Revere\energy_analysis\120924\ASHRAE30pct.PI.Final11_ApartmentMidRise_STD2010_Chicago_woodframe&brick.idf
** Warning ** Object=Building, name=30pct Prototype Mid-Rise
Apartment, entered with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G SW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G SW Apartment
** Severe ** IP: IDF line~7354 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G NW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G NW Apartment
** Severe ** IP: IDF line~7379 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=Office
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=Office
** Severe ** IP: IDF line~7404 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G NE Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G NE Apartment
** Severe ** IP: IDF line~7429 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G N1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G N1 Apartment
** Severe ** IP: IDF line~7454 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G N2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G N2 Apartment
** Severe ** IP: IDF line~7479 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G S1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G S1 Apartment
** Severe ** IP: IDF line~7504 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=G S2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=G S2 Apartment
** Severe ** IP: IDF line~7529 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M SW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M SW Apartment
** Severe ** IP: IDF line~7554 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M NW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M NW Apartment
** Severe ** IP: IDF line~7579 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M SE Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M SE Apartment
** Severe ** IP: IDF line~7604 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M NE Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M NE Apartment
** Severe ** IP: IDF line~7629 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M N1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M N1 Apartment
** Severe ** IP: IDF line~7654 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M N2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M N2 Apartment
** Severe ** IP: IDF line~7679 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M S1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M S1 Apartment
** Severe ** IP: IDF line~7704 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=M S2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=M S2 Apartment
** Severe ** IP: IDF line~7729 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T SW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T SW Apartment
** Severe ** IP: IDF line~7754 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T NW Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T NW Apartment
** Severe ** IP: IDF line~7779 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T SE Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T SE Apartment
** Severe ** IP: IDF line~7804 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T NE Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T NE Apartment
** Severe ** IP: IDF line~7829 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T N1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T N1 Apartment
** Severe ** IP: IDF line~7854 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T N2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T N2 Apartment
** Severe ** IP: IDF line~7879 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T S1 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T S1 Apartment
** Severe ** IP: IDF line~7904 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Invalid Number in Numeric Field#9 (Cooling
Minimum Air Flow), value=DesignDay, in Sizing:Zone=T S2 Apartment
** Warning ** Invalid Number in Numeric Field#13 (Heating
Maximum Air Flow), value=DesignDay, in Sizing:Zone=T S2 Apartment
** Severe ** IP: IDF line~7929 Error detected for
Object=Sizing:Zone
** ~~~ ** Maximum arguments
reached for this object, trying to process ->0<-
** Warning ** Object=Sizing:System, name=Split GSW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GNW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split Office,
entered with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GNE, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GN1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GN2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GS1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split GS2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MSW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MNW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MSE, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MNE, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MN1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MN2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MS1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split MS2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TSW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TNW, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TSE, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TNE, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TN1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TN2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TS1, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Warning ** Object=Sizing:System, name=Split TS2, entered
with less than minimum number of fields.
** ~~~ ** Attempting fill to
minimum.
** Severe ** Possible incorrect IDD File
** ~~~ ** Possible Invalid Numerics
or other problems