Thanks All for their reply. As my project is going for LEED certification and client is intersted in knowing how much savings they will get by spending money on High SRI paint or tile.

p.s Jim, i would appreciate if you share the response on SRI modeling from the Conference case study.

Thanks!

On Thu, Oct 4, 2012 at 1:07 PM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

Brent brings up an excellent point.  You don?t want to model the roof?s performance for ?day 1? of its life.  ASHRAE is saying that you should degrade the performance to reflectance of .45 when the published value is .70.  Section 5.5.3.1 (mentioned by  the excerpt below) cites several ASTM standards that I?m unfamiliar with, but I think the idea is to make sure the product passes an independent performance test ? in order to qualify for using the .45 reflectance.

This does not address how to model the performance of differing SRI values; if I learn anything on that topic, I?ll share it here.

 

?For exterior roofs other than roofs with ventilated attics, the roof surface may be modeled with a reflectance of 0.45 if the reflectance of the proposed design roof is greater than 0.70 and its emittance is greater than 0.75. The reflectance and emittance shall be tested in accordance with the Exception to Section 5.5.3.1. All other roof surfaces shall be modeled with a reflectance of 0.3.?

 



 

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent
Sent: Thursday, October 04, 2012 3:53 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] SRI/Refelectivity study

 

 

For a so-called ?cool roof? change the Material object that is outermost in the Construction object for the roof.  The values to use depend on dirt accumulation, age, type of coating etc, but I usual values are a solar absorptance of 0.45 and a thermal absorptance of 0.75 ( from ASHRAE 90.1-2007 Table 11.3.1 No. 5.c) .

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Javed Iqbal
Sent: Thursday, October 04, 2012 1:24 PM


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] SRI/Refelectivity study

 

 

Thanks for your response. I found a document on Cool roof and it says:

 

"The most important feature of an ideal cool roof is that its surface strongly reflects sunlight. 

The surface of an ideal cool roof should also efficiently cool itself by emitting thermal radiation. 

Thus, a cool roof should have both high ?solar reflectance? (ability to reflect sunlight, measured 

on a scale of 0 to 1) and high ?thermal emittance? (ability to emit thermal radiation, also 

measured on a scale of 0 to 1). The solar reflectance and thermal emittance of a surface are 

called its ?radiative? properties because they describe its abilities to reflect solar radiation and 

emit thermal radiation".  

 

http://coolcolors.lbl.gov/assets/docs/fact-sheets/Cool-roof-Q%2BA.pdf

It means cool roof has both the properties i.e. Thermal reflectance and Solar Reflectance so according to this i need to consider both the values for cool Roof. Please guide me on this..

 

Regards!

On Thu, Oct 4, 2012 at 12:09 PM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:

 

I thought Solar Absorptance was the key input for SRI- 

 

 

 

 

Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions

120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951

www.phasechange.com 

  

 

 

 




On Thu, Oct 4, 2012 at 11:22 AM, Javed Iqbal <eee.javed@xxxxxxxxx> wrote:

 

Hi,

 

I'm trying to see effect of roof reflectivity on Energy consumption and as per I/O guide there are two parameters Thermal absorptance and Visible absorptance which accounts the impact of reflectivity. Can anybody guide me on which value needs to be considered for high SRI/Reflectivity study.

 

Thanks in Advance!

 

--

 

 

Javed Iqbal, LEED AP, CEA

Energy Analyst 

 

 

 

 

 

 

 



 

--

 

 

Javed Iqbal, LEED AP, CEA

Energy Analyst 

 

 

 

 

 

 




--


Javed Iqbal, LEED AP, CEA
Energy Analyst 








__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___