|
Another useful source is Table 1 in this link, http://www1.eere.energy.gov/femp/pdfs/coolroofguide.pdf Note E+ input is absorptance not reflectance and that Absorptance + Reflectance = 1. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes Brent brings up an excellent point. You don’t want to model the roof’s performance for “day 1” of its life. ASHRAE is saying that you should degrade the performance to reflectance of .45 when the published value is .70. Section 5.5.3.1 (mentioned by the excerpt below) cites several ASTM standards that I’m unfamiliar with, but I think the idea is to make sure the product passes an independent performance test … in order to qualify for using the .45 reflectance. This does not address how to model the performance of differing SRI values; if I learn anything on that topic, I’ll share it here. “For exterior roofs other than roofs with ventilated attics, the roof surface may be modeled with a reflectance of 0.45 if the reflectance of the proposed design roof is greater than 0.70 and its emittance is greater than 0.75. The reflectance and emittance shall be tested in accordance with the Exception to Section 5.5.3.1. All other roof surfa
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |