Here are lines used to calculate the ventilation flow rate for the ZoneVentilation:WindandStackOpenArea object, extracted from HVACManager.f90. Qw = Cw*Ventilation(J)%OpenArea*GetCurrentScheduleValue(Ventilation(J)%OpenAreaSchedPtr)*WindExt Qst = Cd*Ventilation(J)%OpenArea*GetCurrentScheduleValue(Ventilation(J)%OpenAreaSchedPtr)* & SQRT(2*9.81*Ventilation(J)%DH*ABS(TempExt-ZMAT(NZ))/(ZMAT(NZ)+273.15)) VVF = SQRT(Qw*Qw + Qst*Qst) Hope this helps. Lixing From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of HJ
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.