Francesco,
I think there used to be two different humidifiers, but there is only one now! (In the USA, it is fairly common to have a humidifier which uses steam from a boiler, so it seems unusual that this option is not available.)
If you are using Baseline #4, then you probably have only one zone for the air loop. If that is true, you should be able to place the humidifier inside the zone by assigning its inlet / outlet air nodes the same as the zone inlet / outlet nodes. Another possibility is to place it on the outlet of the air loop. I have not done this in a model, so I am not sure if this is the best approach.