[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Simulation for LEED - enegy saving using Natural Ventilation
1) That hybridventilation manager works. I've tried it. There is a small documentation descrepancy in what the correct string is in the input field, but is probably corrected since V7.2.
2) LEED does not require the simulation for EAp2 and the Increased Ventilation Credit to be the same one. You could handle them sepetately, and at the end will probably save you lots of time.
3) I find it hard to believe that a 100% naturally ventilated building will meet ASHRAE 55 all of the time.
4) Yes. For EAp2 you'll need to add the baseline system's mechanical systems to the existing model and these should jump on when the natural ventilation is not meeting the loads.
5) Be warned: Control wise this is quite hard to setup. Proving that you meet ventilation requirements for Natural Ventilation is easy. Open all the windows and watch that ventilation rarely falls below minimum requirements. But setting this up so that you meet the loads of a 50 ACH is quite hard. Thus my point of doing two seperate simulations to illustrate two different points.
- Yes we can ventilate well naturally, if we choose to open the windows
- Yes we have energy saving measures in place (ASHRAE 90.1)
If you split the two simulations, you can leave away the AFN for the ASHRAE 90.1 simulation, and duplicate the baseline systems for the proposed design.
It is tempting to try and use the hybrid case, but the proposed design has no hybrid control. Thus your baseline mechanical type systems in your proposed design should operate independant of your natural ventilation.
I've had painfull experiences with this excersice. Anyone else?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "tekton9276" <melissacacciatori@...> wrote:
>
> Hi everybody!
>
> I need to do a simulation that combines Natural Ventilation + HVAC, for LEED certification.
>
> I have already simulated the proposal case with natural ventilation only, and then I could see that the building have 70% of occupied time in confort in compliance with Adaptative Model of Ashrae Standard 55-2010.
>
> Now, I have to include the HVAC system, as it is defined in Ashrae Standard 90.1 - 2007 Appendix G, but this system will be turned on just for the time that Natural Ventilation isn´t enough to thermal comfort.
>
> How is te best way to simulate this hybrid system?
>
> I´ve tried the AvailabilityManager:HybridVentilation, but I couldn´t get reasonable results and some experient professional said that this object doesn´t work...
>
> I have also receieved an indication from this professional, that the best way to do this simulation, is to create a schedule for each hour that the natural ventilation doesn´t met the comfort level. How can I do such schedule? Someone have an example of that?
>
> Thank you all very much for the attention!
>
> Bs,
> Melissa Cacciatori.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/