If global radiation is provided, the
weather converter uses
the Perez split model for direct and diffuse
calculations. If no
global is provided then it uses the Zhang-Huang model to
come up with
Global and then Perez model to split.
I believe all this is described in the Auxiliary
Programs
document.
For design days, there are several solar models
available -- ASHRAE Clear
Sky, ASHRAE Taub (2009 clear sky) and Zhang-Huang.
Along with you
being able to put in your actual beam and diffuse
values, if
desired. The methods are described in the Input Output
Reference
and the Engineering Reference.
At 08:04 AM 11/8/2012, rokkas80 wrote:
Ok. Based
on cloud information
from the weather files, or?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Dru Crawley
<dbcrawley@...> wrote:
>
> The EnergyPlus WeatherConverter now does
calculate direct/diffuse
solar
> radiation if it's missing.
>
>
> On Thu, Nov 8, 2012 at 9:47 AM, rokkas80
<lukas.rokka@...>
wrote:
>
> > **
> >
> >
> > E+ don't model the solar radiation by it
self. You need to have
weather
> > files with measured or/and modeled values.
But E+ may have some
simple
> > "sanity check" (like that there shouldn't be
any
solar radiation during
> > night time and min/max limits).
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
"Jean
marais" <jeannieboef@>
> > wrote:
> > >
> > > no. i mean from latidute and longitude
and the equation of
time, etc.
> > together with some assumptions about
atmospheric conditions,
the direct and
> > diffuse radiation can be calculated. It does
not have to be
measured, or?
> > If there was no weather data for this, or
incorrect weather
data...I was
> > under the impression that e+ runs a "sanity
check" to
see if the radiation
> > from weather files is okay. And if not, it
uses it's calculated
results?
> > I've made a excel spreadsheet once to do
this as a check...and
the results
> > are okay.
> > >
> > > --- In
EnergyPlus_Support@xxxxxxxxxxxxxxx,
"rokkas80" <lukas.rokka@>
> > wrote:
> > > >
> > > > I don't understand what you are
asking for, could you
please clarify?
> > > > Do you mean that e+ calculates the
direct normal
solar from global and
> > diffuse solar? Well, the Weather Converter
program can
calculate the direct
> > normal from global and diffuse solar
according to the
documentation.
> > > >
> > > >
> > > > --- In
EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean
marais" <jeannieboef@>
> > wrote:
> > > > >
> > > > > "Even though the solar data
from STR�NG
varies in quality it's
> > still better, for most sites, than that
provided in the ASHREAE
IWEC files"
> > > > >
> > > > > Doesn't e+ calculate the
direct solar?
> > > > >
> > > > > --- In
EnergyPlus_Support@xxxxxxxxxxxxxxx,
"rokkas80" <lukas.rokka@>
> > wrote:
> > > > > >
> > > > > > Hi all,
> > > > > >
> > > > > > I've updated my tool for
creating Actual
Meteorological Year (AMY)
> > files for North Europe. The tool can be
downloaded at
> >
http://rtwc.blob.core.windows.net/clickonce/publish.htm.
> > > > > >
> > > > > > News for this version,
Real-Time Weather
Converter 2.0:
> > > > > > - All data from ISD is
available, also data
marked as
> > "Additional". If you tried the tool before
but didn't
get any data for your
> > station, you should now be able to get
usable data for most
locations.
> > > > > > - A new server that maps
data from the SMHI
server. Now retrieval
> > time are just a few seconds for one year of
solar data. A
AMY-files can now
> > be made in under a minute.
> > > > > > - Missing data points
are visualized
graphically.
> > > > > >
> > > > > > The tool was made as
part of my MSc degree
project at
> > M�lardalens University, Sweden. It uses
observed actual
weather data from
> > the Integrated Surface Database (ISD),
> >
http://www.ncdc.noaa.gov/oa/climate/isd, and
modeled solar radiation
data
> > from STR�NG,
http://strang.smhi.se.
> > > > > >
> > > > > > Roughly, the tool covers
most of Europe
excluding south Europe.
> > Long-term coverage is from 1 of January 1999
to up to date for
the
> > northernmost area, the southern area is
covered from 1 of June
2006 (see
> > website for map).
> > > > > >
> > > > > > The quality of the solar
radiation data
from STR�NG varies in
> > the geographical dimension. Roughly the
model gives good result
for Sweden
> > and Central Europe, but underestimates for
ocean coast near
areas like UK,
> > Norway etc. The model do underestimate as
well for the Baltics,
northern
> > Finland and some high altitude sites.
There's a validation
figure (for
> > Google Earth) at the tools homepage in the
help section. Even
though the
> > solar data from STR�NG varies in quality
it's still better,
for most
> > sites, than that provided in the ASHREAE
IWEC files (which
underestimate
> > direct solar radiation in the range of 20 to
40 % for the area
in
> > question). For model calibration these data
are very
useful.
> > > > > >
> > > > > > You are free to use the
modeled solar
radiation data from
> > STR�NG. Weather data from ISD may however
have restrictions
regarding
> > commercial usage, depending on country and
what data is being
used. Some
> > countries (UK, Norway, Netherlands, Slovenia
and Sweden from
next year(?))
> > have free weather data, other countries some
restrictions and
some
> > countries have most of their weather data
restricted. There is
a method in
> > the tool that excludes data marked as
"Additional" by
WMO, this should make
> > commercial use of resulting weather files
possible for most
countries (my
> > personal interpretation of WMO resolution 40
Annex I). But it's
up to the
> > end user of the tool to read and interpret
the WMO resolution
40 and check
> > with their National Weather Service for
their data policy. If
intentions
> > are non-commercial the data accessed and
created by this tool
can be used
> > freely for all countries in question.
> > > > > >
> > > > > > The ISD lack recent data
for many of the
German weather stations.
> > Observed weather data can still be acquired
from other sources
(i.e.
> > EnergyPlus real-time weather service,
Wunderground) and by
using copy/paste
> > inserted into the tool. The tool has methods
for re-sampling,
interpolating
> > and filling data gaps.
> > > > > >
> > > > > > This tool was developed
to make AMY-files
to be used for model
> > calibration. But it would be possible to use
a similar approach
to create
> > Typical Metrological Year (TMY) files as
well, at least for the
geographic
> > area where there soon exist 13 years of free
solar radiation
data available
> > free via STR�NG. Let me know if you think
there's a demand
for this kind
> > of weather files or if you know of any
available tools or
algorithms that
> > can make this kind of files.
> > > > > >
> > > > > > Best regards,
> > > > > > Lukas Lundstr�m
> > > > > >
https://sites.google.com/site/weatherconverter
> > > > > >
> > > > >
> > > >
> > >
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a
message to
energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that
not everyone has a
high speed connection. Limit attachments to small
files.
EnergyPlus Documentation is searchable. Open
EPlusMainMenu.pdf
under the Documentation link and press the "search"
button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an
email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/