Thank you for your help so much. I chose pump's Rated Pump Head as well as the Plant Loop Volume as Brent recommended, the difference was a little less than before. However, for some timesteps when the HVAC system started to operate, the difference between "Chiller Evap Heat Trans Rate" and the water enthalpy difference at evaporator will still be very high, about 20%. Is it caused by "some transient output condition" mentioned by Dr. Li, or is there other reason that I didn't consider before? Thanks

Yan 

----- Original Message -----
From: "Brent Griffith" <brent.griffith@xxxxxxxx>
To: "EnergyPlus Support" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, November 14, 2012 3:42:22 PM
Subject: RE: [EnergyPlus_Support] How to calcualte "Chiller Evap Heat Trans Rate" in E+









There are two things you are not considering. First there is pumping of the chilled water, which adds heat to the fluid that the chiller must remove. If you set the pump’s Rated Pump Head to a tiny number this can be removed. Second there is a loop capacitance model which will shift loads over time. If you set the Plant Loop Volume field to a tiny number this can be removed. 







From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Yan Xue 
Sent: Wednesday, November 14, 2012 1:16 PM 
To: EnergyPlus Support 
Subject: [EnergyPlus_Support] How to calcualte "Chiller Evap Heat Trans Rate" in E+ 








Dear all 

I'm trying to figure out how the E+ calculates the chiller electric consumption recently. According to the reference, I learnt that the ratio of "Chiller Evap Heat Trans Rate" to "Chiller Electric Consumption" is COP. And in inputoutput reference, it's said that "Chiller Evap Heat Trans Rate" means the evaporator heat transfer which is the cooling delivered by the chiller. So I think the "Chiller Evap Heat Trans Rate" equals the water enthalpy difference between water inlet node and outlet node of the cooling coil. And it should be the same as the air enthalpy difference between air inlet and air outlet node of the cooling coil. However, when I checked them and found that for most timestep, the difference was very little such as 1%, but sometimes it could be as much as +-20% ! 

Is there anybody who can explain the problem for me? I have attached the idf file and there are 5 zones in the building, I use one single HVAC system for each zone, we can just focus on one zone for the problem. In the "Output:Variable", I have chosen the related parameters for the North Zone. Thank you so much. 

Sincerely 

Yan 








------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/